Table 2. advanced configuraTion Service MenuS (conT.)
MENU
FEATURE
460
Heat Recovery Rate
470
Cool Recovery Rate
480
Minimum Off Time
490
Humidity Control
Enable
(Select models only)
491
Humidity Deadband
500
Programmable/
Intermittent Fan
501
Intermittent Fan On
Time
502
Intermittent Fan Off
Time
510
Power Harvesting
Enable
(For use on systems
in which a Common
"C" power wire is
unavailable)
520
Default Display
Icons
530
Revision
540
Factory Default
Reset
600
System Test Main
Output (Cool)
610
System Test Main
Output (Heat)
620
System Test Fan
Output
630
System Test
Emergency Output
640
System Test
Economizer
© COPYRIGHT 2014 PECO ASTRONICS. ALL RIGHTS RESERVED.
OPTIONS
STD.MODEL
DEFAULT
0-18°F/Hr
0 °F/Hr
0-10°C/Hr
0-18°F/Hr
0°F/Hr
0-10°C/Hr
1-10 minutes
4 minutes
0-3
0
10-50
30% relative
humidity (RH)
0-2
0
1-60 minutes
5 minutes
0-60 minutes
25 minutes
0-3
0
0-4
0
0,1
0
0-2
0
0-3
0
0,1
0
0,1
0
0,1
0
DESCRIPTION / COMMENTS
Defi nes the rate at which the device achieves the heat comfort setpoint. Select 0 to disable ramp
recovery.
Defi nes the rate at which the device achieves the cool comfort setpoint. Select 0 to disable ramp
recovery.
Sets the minimum off time for both the heat and cool output.
Selects how humidity will be controlled. When dehumidify control is enabled, the Y2 terminal becomes
dehumidify. Note: If option 3 is selected, Service Menu 491 becomes available.
0 =
Disabled
1 =
Dehumidify Control
2 =
Humidify Control
3 =
Dehumidify and Humidify Control
Selects the deadband in %RH between the humidify and dehumidify setpoints. Note: If option 3 is
selected in Service Menu 490, Service Menu 491 becomes available.
10; 20; 30; 40; 50
0 =
Disable
1 =
Programmable Fan: Fan operates continuously in occupied periods or with demand in
unoccupied periods.
2 =
Intermittent Fan: Fan operates based on the on and off times set in menus 501 and 502.
Defi nes the on time for the Intermittent Fan.
Defi nes the off time for the Intermittent Fan. Select 0 for continuous fan.
Options 1-3 draw a small amount of current from load wire indicated to supplement battery supply.
0 =
No power harvesting is available.
1 =
Use Y1 as the battery supplement.
2 =
Use W1 as the battery supplement.
3 =
Use both Y1 and W1 as the battery supplement
Select icons that will be displayed in the Default Display screen.
0 =
Time, Temp, SP
1 =
Time, Temp
2 =
Time
3 =
Temp
4 =
None
Displays fi rmware revision information (for technician); not adjustable.
Select 1 (enable) to restore factory default settings for thermostat. Select 0 to disable.
0 =
Disable
1 =
Enable
Note: Press "Done" key to complete process.
Select an option to activate the fan output for 10 minutes; select 0, Done or a different Service Menu
to disable.
0 = Disable
1=
Cool Stage 1
2 =
Cool Stage 2
Select an option to activate the fan output for 10 minutes; select 0, Done or a different Service Menu
to disable. Note: Outputs will be activated based upon the system confi guration.
0 =
Disable (Default)
1 =
Heat Stage 1
2 =
Heat Stage 2
3 =
Heat Stage 3
Select 0 or 1 to activate the fan output for 10 minutes; select 0, Done or a different Service Menu to
disable.
0 =
Disable Fan Output
1 =
1 =
1 =
Enable Fan Output
Enable Fan Output
Enable Fan Output
Note: Outputs will be activated based upon the system confi guration.
Select 0 or 1 to activate the Emergency output for 10 minutes; select 0, Done or a different Service Menu to
disable.
0 =
Disable Emergency Output
1 =
Enable Emergency Output
Select 1 to activate the Economizer output for 10 minutes; select 0, Done or a different Service Menu to
disable.
0 =
Disable Economizer Output
1 =
Enable Economizer Output
4
Warning: Power Harvesting is intended to be used
only as a battery supplement. If enabled, the feature
preserves battery life. If Power Harvesting is not
compatible with your system, select "0" (default) to
disable. If thermostat is powered from AC, select only "0"
or off. Consult a technician if you have questions.