Table 2. advanced configuraTion Service MenuS (conT.)
MENU
FEATURE
290
Range Low
300
Range High
310
Setback Low
320
Setback High
330
Zone Temp Offset
340
Keypad Lockout
341
Enable Pin Access
342
Set PIN Access
Code
350
Fan Mode
Enable
360
System Mode
Enable
370
Economizer/Outside
Air Damper
380
Minimum Deadband
Adjustment
390
Pre-Occupancy
Purge
395
Maximum Override
0=Time until next
Time Limit
400
Cycles Per Hour
(CPH) Cooling
Stage 1
410
Cycles Per Hour
(CPH) Cooling
Stage 2
420
Cycles Per Hour
(CPH) Heating
Stage 1
430
Cycles Per Hour
(CPH) Heating
Stage 2
450
Cycles Per Hour
(CPH) Emergency
Heating &
Stage 3 Heat
© COPYRIGHT 2014 PECO ASTRONICS. ALL RIGHTS RESERVED.
OPTIONS
STD. DEFAULT
50-90 °F or
50°F (10°C)
10-32°C
50-90 °F or
90°F (32°C)
10-32°C
Off; 50-82°F or
55°F (13°C)
11-27°C
Off; 58-90°F or
90°F (32°C)
11-32°C
+/-9°F or +/-
0°F (18 °C)
4.5°C
0-3
0
0,1
0
000-999
000
1-3
3
0-3
1
0-4
0
3-10°F, 1.5-5°C
3°F
0-3 hours
0 hours
3
event; or
1-4 hours
0-6 CPH
0 CPH
0-6 CPH
0 CPH
0-12 CPH
0 CPH
0-12 CPH
0 CPH
0-12 CPH
0 CPH
DESCRIPTION / COMMENTS
Choose the lowest selectable temperature setpoint value.
Choose the highest selectable temperature setpoint value.
Select the heat setpoint for setback mode.
0 =
Off
50-82°F (11-27°C)
Select the cool setpoint for setback mode.
0 =
Off
58-90°F (11-32°C)
Adjusts the displayed value; may differ from actual zone temperature.
Restricts access to certain features of device; Service Menu still available if enabled.
0 =
No key pad lockout (Default)
1 =
Disables Schedule and System keys
2 =
Disables Schedule, System, and Fan keys
3 =
Disables all keys
Applies a 3 digit access code to enter Service Menu 342
0 =
Disable
1 =
Enable
Choose a 3-digit code.
1 =
ON: Fan is turned on regardless of demand.
2 =
Auto: Fan is turned on according to heating or cooling demand.
3 =
ON or Auto: Allows occupant to select either 1 or 2 above.
Allows ability to determine which system modes the occupant can select.
0 =
OFF, Auto (0 is NOT valid for following configurations: Heat Only; Cool Only.)
1 =
OFF, Heat, Cool, Auto
2 =
OFF, Heat, Cool
3 =
Heat, Cool, Auto
0 =
Off
1 =
Time Based Output
2 =
Economizer
3 =
Continuous Outside Air Damper
4 =
Cycled Outside Air Damper
Select a changeover deadband value to prevent short cycling between heating and cooling modes.
The value is adjustable to meet various HVAC system requirements.
Select to energize fan for selected number of hours (0-3) prior to all occupied events.
Restricts the duration that a temporary hold can be set. The temporary hold is limited by the maximum
amount of time as defined in this Service Menu.
0 =
Remainder of time until the next scheduled event.
1 =
1 Hour
2 =
2 Hours
3 =
3 Hours
4 =
4 Hours
Defines the number of cycles per hour for cooling (Stage 1). Select 0 to enable ON-OFF control for
Stage 1 cooling.
Defines the number of cycles per hour for cooling (Stage 2). Select 0 to enable ON-OFF control for
Stage 2 cooling.
Defines the number of cycles per hour for heating (Stage 1). Select 0 to enable ON-OFF control for
Stage 1 heating.
Defines the number of cycles per hour for heating (Stage 2). Select 0 to enable ON-OFF control for
Stage 2 heating.
Defines the number of cycles per hour for heating. Select 0 to enable ON-OFF control for Emergency
Heating & Stage 3 Heat.
3
P/N 70932 3220-2324 REV 00