Model
Terminal
R/L1, S/L2, T/L3
R1/L11, S1/L21, T1/L31
U/T1, V/T2, W/T3
T605
-, +3
R/L1, S/L2, T/L3
R1/L11, S1/L21, T1/L31
U/T1, V/T2, W/T3
T720
-, +3
*1
Remove insulation from the ends of wires to expose the length of wire shown.
*2
A junction terminal is necessary to connect a braking resistor unit (LKEB-series) to terminals - and +3.
■
Connect a Fuse to the Input Side (Primary Side)
The drive circuit protection must comply with IEC/EN 61800-5-1:2007 for protection against a short circuit in the
internal circuitry. Yaskawa recommends connecting semiconductor protection fuses on the input side for branch
circuit protection.
WARNING
Electrical Shock Hazard. After the drive blows a fuse or trips a GFCI, do not immediately energize the drive or
operate peripheral devices. Wait for the time specified on the warning label at a minimum and make sure that all indicators are OFF.
Then check the wiring and peripheral device ratings to find the cause of the problem. If you do not know the cause of the problem,
contact Yaskawa before you energize the drive or peripheral devices. If you do not fix the problem before you operate the drive or
peripheral devices, it can cause serious injury or death.
6-Phase/12-Pulse 400 V Class
Table 13.2 Factory-Recommended Branch Circuit Protection (6-Phase/12-Pulse 400 V Class)
Drive Model
T103
T140
T168
T208
T250
T302
YASKAWA TOEPC71061782C GA800 Drive Installation & Primary Operation
Recomm. Gauge
Applicable Gauge
mm
2
70 × 2 × 2
95 × 4
70 × 4
95 × 2
95 × 2 × 2
95 × 4
70 × 4
95 × 2
Semiconductor Protection Fuse
Model
Manufacturer: EATON/Bussmann
FWH-200B
FWH-225A
FWH-225A
FWH-275A
FWH-300A
FWH-350A
Wire Stripping
*1
Length
mm
2
mm
70 - 150
-
70 - 150
-
35 - 125
-
60 - 150
-
70 - 150
-
70 - 150
-
35 - 125
-
60 - 150
-
Drive Model
T371
T414
T477
T568
T605
T720
13 European Standards
Terminal Screw
Tightening Torque
Size and Shape
N∙m (lbf∙in)
35
M12
(310)
35
M12
(310)
35
M12
(310)
32 - 40
M12
(283 - 354)
35
M12
(310)
35
M12
(310)
35
M12
(310)
32 - 40
M12
(283 - 354)
Semiconductor Protection Fuse
Model
Manufacturer: EATON/Bussmann
FWH-400A
FWH-450A
FWH-600A
FWH-600A
FWH-800A
FWH-800A
71