A - Load Impedance
• Use in sinking mode
The external power supply changes the voltage level of the pulse train output signal. Keep the voltage from an
external source between 10.8 Vdc to 16.5 Vdc. Adjust the load impedance to keep the current at 16 mA or lower.
External Power Supply (V)
10.8 Vdc to 16.5 Vdc
A - External power supply
B - Load Impedance
■
Set Sinking Mode/Sourcing Mode
Close the circuit between terminals SC-SP and SC-SN to set the sinking mode/sourcing mode and the internal/
external power supply for the MFDI terminals. The default setting for the drive is internal power supply sinking
mode.
NOTICE
Damage to Equipment. Do not close the circuit between terminals SP-SN. If you close the circuits between
terminals SC-SP and terminals SC-SN at the same time, it will cause damage to the drive.
YASKAWA TOEPC71061782C GA800 Drive Installation & Primary Operation
Figure 10.12 Wiring to Use Pulse Train Output in Sourcing Mode
Load Impedance (kΩ)
Figure 10.13 Wiring to Use Pulse Train Output in Sinking Mode
1.0 kΩ or more
C - Sinking current
10 Drive Start-Up
Sinking current (mA)
16 mA maximum
49