Area Of Use - YASKAWA T103 Installation & Primary Operation

Ac drive for industrial applications
Table of Contents

Advertisement

Item
Electronic circuit protection
Note:
Ground Fault
This protection detects ground faults during run. The drive will not provide protection when:
Protection
• There is a low-resistance ground fault for the motor cable or terminal block
• Energizing the drive when there is a ground fault.
DC Bus Charge LED Charge LED illuminates when DC bus voltage is more than 50 V.
Optional
Braking Transistor
DC Link Choke
Optional
Item
Indoors

Area of Use

Overvoltage Category III
Permitted frequency fluctuation: ±5%
Power Supply
Permitted voltage fluctuation: -15% to +10%
Three-phase AC power supply 380 V to 480 V at 50/60 Hz
IP00/UL Open Type: -10 °C to +50 °C (14 °F to 122 °F)
• When you install the drive in an enclosure, use a cooling fan or air conditioner to keep the internal air temperature in the permitted range.
Ambient Temperature
Setting
• Do not let the drive freeze.
• You can use IP00/UL Open Type drives at a maximum of 60 °C (140 °F) when you derate the output current.
95% RH or less
Humidity
Do not let condensation form on the drive.
Storage Temperature -20 °C to +70 °C (-4 °F to +158 °F) (short-term temperature during transportation)
Pollution degree 2 or less
Install the drive in an area without:
• Oil mist, corrosive or flammable gas, or dust
• Metal powder, oil, water, or other unwanted materials
Surrounding Area
• Radioactive materials or flammable materials, including wood
• Harmful gas or fluids
• Salt
• Direct sunlight
1000 m (3281 ft) Maximum
Note:
Derate the output current by 1% for each 100 m (328 ft) to install the drive in altitudes between 1000 m to 4000 m (3281 ft to 13123 ft).
Altitude
It is not necessary to derate the rated voltage in these conditions:
• When you install the drive at 2000 m (6562 ft) or lower
• When you install the drive between 2000 m to 4000 m (6562 ft to 13123 ft) and ground the neutral point on the power supply.
Contact Yaskawa or your nearest sales representative if you will not ground the neutral point.
• 10 Hz to 20 Hz: 1 G (9.8 m/s
• 20 Hz to 55 Hz:
Vibration
T103 to T168: 0.6 G (5.9 m/s
T208 to T720: 0.2 G (2.0 m/s
Installation
Install the drive vertically for sufficient airflow to cool the drive.
Orientation
Item
• UL61800-5-1
• EN61800-3
Harmonized Standard
• IEC/EN61800-5-1
• Two Safe Disable inputs and one EDM output according to EN ISO 13849-1:2015 (PL e (Cat.III)), IEC/EN61508 SIL3
• IP00/UL Open Type
Enclosure Protection
Design
• IP55/UL Type 12
Area of Use
Install this product in a location with Overvoltage Category III and pollution degree 2 or less as specified in UL 508C.
YASKAWA TOEPC71061782C GA800 Drive Installation & Primary Operation
Table 5.3 Environment
2
, 32.15 ft/s
2
)
2
, 19.36 ft/s
2
)
2
, 6.56 ft/s
2
)
Table 5.4 Standard
5 Common Drive Specifications
Specification
Specification
Specification
13