Peco T190 Installation Instructions Manual page 4

Hide thumbs Also See for T190:
Table of Contents

Advertisement

Available languages

Available languages

TABLE: SERVICE MENU FUNCTIONS
Note: All menu numbers may not appear, depending upon the T190 model.
MENU
FEATURE
1
F / C Display
4
Range Limit Low
5
Range Limit High
8
Zone Temp Offset
9
Keypad Lock
17
Minimum Deadband
Adjust
18
Factory Default
Reset
20
Reversing Valve
Type
21
System Type
22
Heat Stages
23
Cool Stages
30
Cycles Per Hour
(CPH) for First Stage
Compressor
31
Cycles Per Hour
(CPH) for Second
Stage Compressor
32
Cycles Per Hour
(CPH) for First Stage
Heat
33
Cycles Per Hour
(CPH) for Second
Stage Heat
34
Cycles Per
Hour (CPH) for
Emergency Heat
35
Heat Recovery Rate
36
Cool Recovery Rate
© COPYRIGHT 2009 PECO, INC. ALL RIGHTS RESERVED.
RANgE
STD.
DESCRIPTION / COMMENTS
MODEL
DEFAULT
°F or °C
°F
Sets the temperature display in Fahrenheit (F) or Celsius (C).
50-90°F,
50°F
Sets the lowest value the user can select for the setpoint.
10-32°C
50-90°F,
90°F
Sets the highest value the user can select for the setpoint.
10-32°C
+/- 9°F,
0°F
Zone Temperature offset adjusts the sensed Zone Temperature reading from the A to
+/- 4.5°C
D converter, allowing calibration in the field.
0-3
0= OFF
Allows you to choose what the occupant can access. The Service Menu is still
available if Key Pad Lock Out is ON.
0= OFF= No keypad lockout.
1= ON1= Disables all functions except the System key, Temporary Override and
Permanent Override.
2= ON2= Disables all functions except Temporary Override and Permanent Override.
3= ON3= Disables all functions.
3-9°F,
3°F
Sets the minimum difference between the Cool and Heat Setpoints (Deadband). Heat
1.5-5°C
and Cool setpoints are to be adjusted as equally as possible to meet the Minimum
Deadband and Range Limits. The Minimum Deadband must not exceed the (Range
Limit High – Range Limit Low).
0-1
0= OFF
0= OFF= No reset.
1= DFLT= Resets to Factory Default; retains only clock settings.
0-1
0= O
0= O= Energize on Cool or Deadband (not heat)
1= B= Energize on Heat or Deadband (not cool)
0-1
0= CV
0= CV= Conventional System Logic
1= HP= Heat Pump Logic
1-2
2
1-2
2
0-6 CPH
3 CPH
Applies to Heat Pump or Conventional Cooling, 0 disables cycling
0-6 CPH
3 CPH
Applies to Heat Pump or Conventional Cooling, 0 disables cycling
0-12 CPH
5 CPH
Applies to Conventional Heating only, 0 disables cycling
0-12 CPH
5 CPH
Applies to Conventional Heating, and second stage of heat in 2H1C Heat Pump (Y2
output) only, 0 disables cycling
Applies to Heat Pumps only, 0 disables cycling
0-18°F/Hr
5°F/Hr
0 disables ramp recovery, uses step response
0-10°C/Hr
3°C/Hr
0-18°F/Hr
5°F/Hr
0 disables ramp recovery, uses step response
0-10°C/Hr
3°C/Hr
P/N 69535 3220-2151 REV 0 PAGE 4