3.5
Gas train - pilot connection
The burner is fitted with a dedicated gas train that is fixed to the pipe coupling.
 It should be connected to the main train downstream the filter or the pressure regulator (depending on configuration).
Gas supply pressure 68 - 500 mbar.
WARNING
3.6
Ignition pilot
For proper operation, adjust gas pressure (measured at pressure test point) to 16 mbar (7.3 Nm
Check pilot flame stability before starting up the main burner.
In case of ignition problems, verify:
 the correct positioning of the ignition electrode;
 the gas pressure according to the indications.
3.7
Position of electrode
Place the electrode on the ignition pilot observing
the dimensions specified in Fig. 14.
WARNING
3
CHAPTER
Installation
20065104
71.5
0
18.5
- 2
Diffuser
Fig. 13
3
/h).
± 1
D9218
Electrode
Fig. 14
11