STOVE PERFORMANCE
Please refer to the table in the main instruction manual for details of the stoves' performances
PREPARATORY WORK AND SAFETY CHECKS
IMPORTANT WARNING
This stove must not be installed into a chimney that serves any other heating appliance.
There must not be an extractor fan fitted in the same room as the stove as this can cause the
stove to emit fumes into the room.
Chimney
In order for the stove to perform satisfactory the chimney height must be sufficient to ensure an
adequate draught of approximately 15 Pa so as to clear the products of combustion and prevent
smoke problems into the room.
NOTE: A chimney height of not less than 4.5 metres measured vertically from the outlet of the
stove to the top of the chimney should be satisfactory. Alternatively the calculation procedure
given in EN 13384-1 may be used as the basis for deciding whether a particular chimney design
will provide sufficient draught.
The outlet from the chimney should be above the roof of the building in accordance with the pro-
visions of Building Regulations
Approved Document J.
If installation is into an existing chimney then it must be sound and have no cracks or other faults
which might allow fumes into the house. Older properties, especially, may have chimney faults or
the cross section may be too large i.e. more than 230 mm x 230 mm. Remedial action should be
taken, if required, seeking expert advice, if necessary. If it is found necessary to line the chimney
then a flue liner suitable for solid fuel must be used in accordance with Building Regulations Ap-
proved Document J.
Any existing chimney must be clear of obstruction and have been swept clean immediately before
installation of the stove. If the stove is fitted in place of an open fire then the chimney should be swept
one month after installation to clear any soot falls which may have occurred due to the difference in
combustion between the stove and the open fire.
If there is no existing chimney then any new system must be to the designation described above
and in accordance with Building Regulations Approved Document J.
A single wall metal fluepipe is suitable for connecting the stove to the chimney but is not suita-
ble for use as the complete chimney. The chimney and connecting fluepipe must have a minimum
diameter of 150 mm and its dimension should be not less than the size of the outlet socket of the
stove.
Any bend in the chimney or connecting fluepipe should not exceed 45°. 90° bends should not be
used.
Combustible material should not be located where the heat dissipating through the walls of fireplaces
or flues could ignite it. Therefore when installing the stove in the presence of combustible mate-
rials due account must be taken of the guidance on the separation of combustible material given
in Building Regulations Approved
Document J and also in these stove instructions.
If it is found that there is excessive draught in the chimney then a draught stabiliser should be
fitted. Fitting of a draught stabiliser will affect the requirement for the permanent air supply into
the room in which the stove is fitted in accordance with Approved Document J (see also combu-
stion air supply).
Adequate provision e.g. easily accessible soot door or doors must be provided for sweeping the
chimney and connecting fluepipe where it is not intended for the chimney to be swept through the
appliance.
Hearth
The hearth should be able to accommodate the weight of the stove and its chimney if the chim-
ney is not independently supported. The weight of the stove is indicated in the brochure.
The stove should preferably be installed on a non-combustible hearth of a size and construction
that is in accordance with the provisions of the current Building Regulations Approved Document
J.
The clearance distances to combustible material beneath, surrounding or upon the hearth and
walls adjacent to the hearth should comply with the guidance on the separation of combustible
41