Copying A Day; Setpoint Limits - Honeywell T7350 User Manual

Commercial programmable thermostat for single- or multi-stage conventional/heat pump systems
Hide thumbs Also See for T7350:
Table of Contents

Advertisement

4. Press Run Schedule.
IMPORTANT
— Invalid holidays are ignored.
— Valid holidays require valid: month, day and duration.
— Holidays such as the fifth Tuesday of a month with
only four Tuesdays are also invalid.

Copying a Day

,
Use the PDA
TStatSpec, or keys in the "Schedule" area of the
keypad for this procedure:
1. Press Occupied.
2. Press Day to select the day to be copied.
3. Press Copy.
4. Press Copy again. The following day is automatically
selected. (For example: If the day to be copied is
Monday, Tuesday will automatically be selected.)
5. If necessary, press Day until the day to receive the copy
is displayed.
NOTE: To cancel the copy press Run Schedule before
step 6.
6. Press Copy.
NOTE: DONE displays for two seconds then the
program display reappears.
7. Repeat steps 2 through 6 for all the days desired.
8. Press Run Schedule.
Clearing Program Start Times
1. Press Occupied or Not Occupied until the start period to
be cleared is displayed.
2. Press Day until desired day is displayed.
3. Press Clear Start Time.
4. Repeat steps 1 through 3 for all the start times to be
cleared.
5. Press Run Schedule.
Temperature Setpoints

Setpoint Limits

The setpoint temperature range is 40°F to 90°F (4°C to 32°C)
for heating and 45°F to 99°F (7°C to 37°C) for cooling.
NOTES: The ranges mentioned can be limited based upon
setpoints and stops:
1.
The greater of the Minimum Heat Stop and the Not
Occupied Heat setpoints determines the
lowest setting to which the occupied heat setpoint
can be adjusted:
°F: Stop/NotOcc ≤ OccHeat ≤ (OccCool - 2).
°C: Stop/NotOcc ≤ OccHeat ≤ (OccCool - 1).
2.
The lesser of the Maximum Cool Stop and Not
Occupied Cool setpoints determines the highest
setting to which the occupied cool setpoint can be
adjusted:
°F: Stop/NotOcc ≥ OccCool ≥ (OccHeat + 2).
°C: Stop/NotOcc ≥ OccCool ≥ (OccHeat + 1).
3.
The Maximum Occupied Heat Setpoint is limited
by Occupied Cool Setpoint – 2° F (1° C).
4.
The Minimum Occupied Cool Setpoint is limited by
the Occupied Heat Setpoint + 2° F (1° C).
T7350 COMMERCIAL PROGRAMMABLE THERMOSTAT
Programming Temperature Setpoints
1. Press Occupied Heat.
2. Press up ▲ or down ▼ until the desired
temperature is displayed.
3. Press Occupied Cool.
4. Press up ▲ or down ▼ until the desired
temperature is displayed.
5. Press Not Occupied Heat.
6. Press up ▲ or down ▼ until the desired
temperature is displayed.
7. Press Not Occupied Cool.
8. Press up ▲ or down ▼ until the desired
temperature is displayed.
9. Press Run Schedule.
Temperature Setpoint Overrides
IMPORTANT
— The setup determines the duration of Occupied
overrides.
— Default duration is three hours.
NOTE: To cancel the Override and immediately return to
the program, press Run Schedule.
TR23 Setpoint Knob
A TR23 setpoint knob can remotely adjust the T7350 setpoint.
Adjustment can be made with the sensor in override.
NOTES:
During override, only occupied and standby heat
setpoints, and cool setpoints are adjusted.
The maximum adjustment is ±5° F (3° C).
With a disconnected or failed TR23, or a T7350 not
set for remote+setpoint, offset is zero.
T7771 Setpoint Button
A T7771 setpoint button can remotely adjust the T7350
setpoint. Adjustment can be made with the sensor in override.
NOTES:
During override, only occupied and standby heat
setpoints, and cool setpoints are adjusted.
The maximum adjustment is ±3° F (2° C).
With a disconnected or failed T7771, or a T7350
not set for remote+setpoint, offset is zero.
Changing Temperature Setpoint Until Next
Program Period
This is a simple change to perform even with the door closed:
1. Press up ▲ or down ▼ until the desired
temperature is displayed.
NOTE: If done while in Standby or Not Occupied mode,
Temporary Occupied override engages
2. The temporary temperature appears for approximately
ten seconds, then the room temperature is displayed.
Using Temporary Occupied Override
The Temporary Occupied Override can be used when the
T7350 is in Not Occupied or Standby mode. It switches to the
Occupied mode for a fixed number of hours.
17
63-2605—09