Honeywell T7350 User Manual page 38

Commercial programmable thermostat for single- or multi-stage conventional/heat pump systems
Hide thumbs Also See for T7350:
Table of Contents

Advertisement

T7350 COMMERCIAL PROGRAMMABLE THERMOSTAT
Factory
Configuration
Option
Default
RoomTemp
Local
RoomRelHumidity
a
Discharge AirTemp None
Outdoor AirTemp
None
OccSensor
0
AuxDO
Time of Day
Key Pad (Lockout)
Enable All
Recovery Heat
5° F/hr
RampMin
Recovery Heat
8° F/hr
RampMax
Recovery Cool
3° F/hr
RampMin
Recovery Cool
6° F/hr
RampMax
Recovery Heat
0° F
OAT@Min
Recovery Heat
40° F
OAT@Max
Recovery Cool
90° F
OAT@Min
Recovery Cool
70° F
OAT@Max
Demand Limit
3° F
Control Bump
Power Failure Seq
0 (x10 sec)
Start
Enable DAT High
None
Limit
Enable DAT Low
None
Limit
High Limit DAT
110° F
Setpoint
Low Limit DAT
45° F
Setpoint
Dehumidification
None
Min On
63-2605—09
Table 20. Thermostat Setup Options Through PDA. (Continued)
PDA
a
Tool CnfgID
X
X
Room Temperature Input
Local: Use internal sensor; TR21/TR24: Use remote sensor.
TR22/TR23: Use remote sensor with setpoint adjustment capability (requires
PDA or TStatSpec software and USB-TIM/U cable).
T7771: Use remote sensor with setpoint adjustment capability (requires PDA
or TStatSpec software and USB-TIM/U cable); changes T7771 LED and
bypass button operation: LED on means either occupied or bypass, pushing
bypass can cancel bypass.
X
X
Room Relative Humidity Input.
None: No humidity sensor; Local: Use internal humidity sensor;
Remote: Use remote humidity sensor (0-10 Vdc signal).
X
X
Discharge Air Temperature Input.
None: No discharge air sensor; or Remote: Remote discharge air sensor.
X
X
Outdoor Air Temperature Input.
None: No outdoor air sensor; or Remote: Remote outdoor air sensor.
X
X
None: No occupancy sensor; or Remote: Remote occupancy sensor.
X
X
Auxiliary Contact Operation:
Time of Day, Economizer, Dehumid Hot Gas BP, or Simple Dehumid.
Auxiliary contact not available if heat pump selected with T7350A.
X
X
Keypad lockout enable/disable through special keypad sequence.
Enable All (0): No lockout.
SetPts & Ovrrd (1): Lockout all keys except: Temporary (Not) Occupied, 5, 6
and
Info Only (2): Lockout all keys except
The special keypress features are never locked out.
X
Minimum heating recovery ramp rate. Range: 0 to 20° F/hr.
X
Maximum heating recovery ramp rate. Range: 0 to 20° F/hr.
X
Minimum cooling recovery ramp rate. Range: 0 to 20° F/hr.
X
Maximum heating recovery ramp rate. Range: 0 to 20° F/hr.
X
Minimum heating outdoor air temperature. Range: -20 to 100° F.
X
Maximum heating outdoor air temperature. Range: -20 to 100° F.
X
Minimum cooling outdoor air temperature. Range: -20 to 100° F.
X
Maximum cooling outdoor air temperature. Range: -20 to 100° F.
X
Demand limit control set point bump. Range: 0 to 10° F.
X
X
Delays start of equipment (fan, heat, cool) after power restored to thermostat.
Range: 0 to 150 seconds (in 10-second increments).
X
X
None: No Discharge Air Temperature (DAT) high limit; Enable: Use DAT High
Limit.
X
X
None: No Discharge Air Temperature (DAT) low limit; Enable: Use DAT Low
Limit.
X
Discharge Air Temperature High Limit Setpoint. Range: 65 to 140° F.
X
Discharge Air Temperature Low Limit Setpoint. Range: 35 to 60° F.
X
X
None: No Minimum On Time dehumidification;
Enable: Dehumidification using Minimum On Time.
Description
.
38
.