T7350 COMMERCIAL PROGRAMMABLE THERMOSTAT
Table 7. T7350H Subbase for Modulating Systems with
Network Communications.
Terminal
24 VAC Cooling transformer.
a
RC
24 VAC Heating transformer.
a
RH
X
Common.
Auxiliary relay connection (normally open).
b
b
aux
aux
Auxiliary relay connection (common).
b
b
aux
aux
W1
Stage 1 heating relay.
Y1
Stage 1 cooling relay.
MX
Modulating common.
MH
Modulating heating signal (4-20 mA).
MC
Modulating cooling signal (4-20 mA).
AS
Discharge Air Sensor connection (1).
AS
Discharge Air Sensor connection (2).
OS
Outdoor Air Sensor connection (1).
OS
Outdoor Air Sensor connection (2).
G
Fan relay.
T3
TR20 Series remote sensor connection (GND).
T4
TR20 Series remote sensor connection (Sensor).
T5
TR20 Series remote sensor connection (Set Pt).
T6
TR20 Series remote sensor connection (Bypass).
T7
TR20 Series remote sensor connection (LED).
HS
Humidity Sensor connection (signal: 0-10 Vdc).
HC
Humidity Sensor connection (common).
HP
Humidity Sensor connection (power).
M
Motion Sensor connection (1).
M
Motion Sensor connection (2).
ebus ebus LonWorks Bus (1).
ebus ebus LonWorks Bus (2).
a
Factory jumper between RC and RH for systems with one
transformer.
b
Floating auxiliary contact (not connected to transformer hot or
common).
63-2605—09
Description
Table 8. T7350M Subbase for Modulating Systems.
Terminal
— 24 VAC Cooling transformer.
a
RC
— 24 VAC Heating transformer.
a
RH
X
— Common.
aux
— Auxiliary relay or 2nd stage of heating or cooling.
W1
— Stage 1 heating relay.
Y1
— Stage 1 cooling relay.
MX
— Modulating common.
MH
— Modulating heating signal (4-20 mA).
MC
— Modulating cooling signal (4-20 mA).
AS
— Discharge Air Sensor connection (1).
AS
— Discharge Air Sensor connection (2).
OS
— Outdoor Air Sensor connection (1).
OS
— Outdoor Air Sensor connection (2).
G
— Fan relay.
T3
— TR20 Series remote sensor connection (GND).
T4
— TR20 Series remote sensor connection (Sensor).
T5
— TR20 Series remote sensor connection (Set Pt).
T6
— TR20 Series remote sensor connection (Bypass).
T7
— TR20 Series remote sensor connection (LED).
HS
— Humidity Sensor connection (signal: 0-10 Vdc).
HC
— Humidity Sensor connection (common).
HP
— Humidity Sensor connection (power).
M
— Motion Sensor connection (1).
M
— Motion Sensor connection (2).
a
Factory jumper between RC and RH for systems with one
transformer.
Mounting Thermostat on Subbase
(Fig. 8)
With the subbase installed, mount the thermostat:
1. Engage the tabs at the top of the thermostat and
subbase.
2. Swing the thermostat down.
3. Press the lower edge of the case to latch.
NOTE: To remove the thermostat from the wall, first pull
out at the bottom of the thermostat; then
remove the top.