Alarm.Com Building 36 ADC-T3000 Manual page 11

Z-wave smart thermostat

Advertisement

Thermostat Z-Wave Specification
5.1.29 0x1D : Current Relay State (READ ONLY)
• Loads – 1 = load, 0 = no load
• State – 1 = closed, 0 = all other state
• Size 4 byte
Bits
7
Z1
Loads
Override
Z1
State
5.1.30 0x1E : Remote Temperature Enable
• When reading, the second byte is the remote temperature status
o 0x00 : Remote temperature disabled
o 0x01 : Active and functioning properly
o 0x02 : Inactive, timeout reached (see parameter 0x27)
o 0x03 : Inactive, temperature differential reached (See parameter 0x28)
o 0x04 : Inactive, 3 successive communication attempts failed
• 0x00 - Disabled (DEFAULT)
• 0x01 - Enabled
• Size 1 byte
5.1.31 0x1F : Heat Differential (1.0°F to 10.0°F), 0.5°F increments
• Default 3.0°F
• Size 4 bytes
5.1.32 0x20 : Cool Differential (1.0°F to 10.0°F), 0.5°F increments
• Default 3.0°F
• Size 4 bytes
5.1.33 0x21 : Temperature Reporting Threshold (0.5°F to 2.0°F), 0.5°F increments
• Default 1.0°F
• Size 4 bytes
5.1.34 0x22 : RESERVED
6
5
4
Y2
Y
-
-
Y2
Y
Building 36 Technologies
An Alarm.com Company
3
2
W2
W
C
RC
W2
W
RC
June 26, 2019
1
0
G
O
RH
Z2
G
O
RH
Z2
-
B
-
B
11