Thermostat Z-Wave Specification
5.1.24 0x18 : HVAC Modes Enabled (Off | Heat | Cool | Auto | Emergency Heat)
• Bitmask
o Bit 0 - Off
o Bit 1 - Heat
o Bit 2 - Cool
o Bit 3 - Auto
o Bit 4 - Emergency Heat
• Allowed Values
o 0x03 - Off, Heat
o 0x05 - Off, Cool
o 0x07 - Off, Heat, Cool
o 0x0F - Off, Heat, Cool, Auto (DEFAULT)
o 0x1F - Off, Heat, Cool, Auto, Emergency Heat
o 0x17 - Off, Heat, Cool, Emergency Heat
o 0x13 - Off, Heat, Emergency Heat
• Size 1 byte
5.1.25 0x19 : Configurable Terminals Setting (W3 | H | DH | Vent)
• 0x00 - None (DEFAULT)
• 0x01 - W3, 3
rd
• 0x02 – H, Humidifier
• 0x03 – DH, Dehumidifier
• 0x04 – External Air Baffle or Vent
• Size 2 byte
5.1.26 0x1A : Power Source (mains | battery) READ ONLY
• 0x00 - Battery
• 0x01 - C-Wire
• Size 1 byte
5.1.27 0x1B : Battery Alert Threshold Low (0-100%)
• Default 30%
• Size 1 byte
5.1.28 0x1C : Battery Alert Threshold Very Low (0-100%)
• Default 15%
• Size 1 byte
Stage Auxiliary Heat
Building 36 Technologies
An Alarm.com Company
June 26, 2019