6 Install the new battery.
a Using both hands, slide the battery about 5 cm (2 in.) into the slot.
b Using the pull handles, push the battery into the slot completely.
c Tighten the four captive screws.
7 Replace the controller unit bezel, as shown in
8 Run the system for at least 24 hours to properly charge the batteries.
The battery can take up to 15 minutes to complete its self-test and up to 24 hours to
fully charge, especially after a power loss of more than a few minutes. When properly
charged, both full-charge indicator lights on the front of the battery are on.
9 Check the battery indicator lights, as shown in
Full Charge-B
Full Charge-A
Note: If either the Full Charge-A or the Full Charge-B indicator light is blinking, the
battery is in the process of charging.
10 Reset the battery installation date using the storage-management software. The
software continues to issue battery-related errors if the installation date is not reset.
38
IBM Netfinity FAStT500 RAID Controller Enclosure Unit User's Reference
Fault-B
Fault-A

Figure 20. Battery CRU indicator lights

CONTAINS
SEALED LEAD
BATTERY.
BATTERY
MUST BE
RECYCLED.
Pb
Figure 7 on page
11.
Figure
20.