How To Test The Z-Wave Device - Axis T8341 User Manual

Pir motion sensor
Hide thumbs Also See for T8341:
Table of Contents

Advertisement

AXIS T8341 PIR Motion Sensor

How to test the Z-Wave device

How to test the Z-Wave device
Warm-up
It will take the motion sensor approximately 2 minutes to warm up after the battery is inserted. During this period the LED behind the
lens will turn on. When the red LED turns off, the warm-up procedure is completed and the device is ready to detect.
This will not affect the Inclusion/Exclusion process.
After you remove the batteries, wait 5 seconds before you refit them.
Quick test
1. If the tamper switch is not pressed after inclusion, the device will enter "Test mode" to allow you to test the device
before it is mounted on the wall.
2. If movement is detected during "Test mode", the LED on the motion sensor will light up once indicating that the unit is
working properly. Retrigger time is about 5 sec.
3. To exit "Test mode" and enter normal mode, simply press the tamper switch for more than 10 seconds.
4. When the PIR is triggered during normal mode the red LED will not light up, and retrigger time is based on a set up value.
Note
Important! Make sure you have created a Z-Wave controller-event linked to the battery-status signal. That way you will
get a notification or a LED indication when a device runs on low battery power.