T9600
INSTRUCTIONS
On/Off Setting: Press
to turn on, press again to turn off, close the fan and valve.
Mode Selection: Press M to change the working mode,
heating mode.
is available only for 4-pipe application or 2-pipe application when BI-FUNCTION is Change Over Sensor
input.
Temperature Setting: Press either
Fan Speed Adjustment: Press
Note: Fan stops at Floor Heating Mode, until FH-FAN parameter set to enable, for single stage floor heating application only.
Delay On/Off setup: Press and hold
then press
or
to adjust the minute by 30 minutes.
Note: Time-On/Off setting performs only once within one day.
Delay On/Off Cancel: Press and hold
delay time, then press
Lock setup: If
Lock function is enabled, the thermostat locks automatically after 30 seconds unused.
Unlock function: Press and hold the
button 5 seconds to unlock instead.
Tio2/ESP Manual: When Tio2/ESP function is set to Manual, press
USER SETTING
Press
and
button for 5 seconds at power off mode to get in parameter list. Press
the list and use
and
button to change parameter value. For T9603-T000-1JF0, press and hold
list and press
to scroll foward through the list.
PARAMETER SETTING (PART 1/2)
T9600-
T9603-
T9601-
TF20-
T000-
TF20-
Code
1JS0
1JF0
1JS0
■
■
■
02
■
■
■
04
■
■
■
05
■
■
06
■
■
■
07
■
08
■
09
■
10
■
■
■
11
■
■
■
12
■
■
13
■
■
■
15
...Continued...
P/N 24-11447-00004 Rev. B Issue Date: 11 2020
or
button to increase or decrease the temperature by 0.5°C/1°F.
to switch the fan mode, auto
button 5 seconds, then "ON" appears, press
button 5 seconds, then "ON" appears, press
or
adjust the time to "00:00".
button 5 seconds to unlock. T9603-T000-1JF0 has no
T9600-
TF21-
1JS0
Parameter name
■
MAC (Modbus)
■
MUTE
■
OFFSET
■
UNOCC-CLG-SP
■
UNOCC-HTG-SP
■
SMPL-TM
■
PB
■
KI
■
BL-TIMER
■
PWR-F-RSTT
TIO2ESP-CTL
■
BAUD_MODBUS
for cooling,
for heating,
flash, high
, medium
button once, to switch Tio2/ESP On or Off.
to scroll forward and M button to scroll backward in
Default
Function
Mac address for Modbus
01
1-96
Enable/disable the beep when push touch button:
00
00: Disable
01: Enable
Offset to be compensate the room temperature:
0°C/
Step: 0.5°C (1°F)"
0°F
Range: 5°C~-5°C (9°F- -9°F)
Cooling setpoint unoccupied mode.
26°C/
Not available for Boiler application
Step: 0.5°C (1°F)
79°F
Range: 22°C~32°C (72°F-90°F)
Heating setpoint unoccupied mode.
18°C/
Step: 0.5°C (1°F)
64°F
Range: 10°C~21°C (50°F-70°F)
Sample time,
10 s
PID parameter, only for PID
Range: 1~99 s
Proportion band,
5
PID parameter, only for PID
Range: 1~10
Integration parameter,
10
PID parameter, only for PID
Range: 0~99
Backlight timer.
30
Range: 0~99 s
Restart after power failure:
00: OFF
02
01: ON
02: Recovery
TIO2ESP control:
00: Automatic
00
01: Manual
For TIO2ESP application
Baud rate for Modbus:
00
00: 9600
01: 4800
English
for venting,
for auto cooling or
, low
fan.
button to switch On or Off delay,
button to switch to check On or Off
button, press and hold the
for 3 seconds to access the parameter