PARAMETER SETTING (PART 2/2)
T9200-
T9200-
Code
TB21-1JS0
TF20-1JS0
17
18
19
21
22
Note
• Terminal blocks changes depending on the application selected, please check the table beside first
• The relay output are line voltage, they are connected with Terminal "L" internally
• The digital input "OCC" can assume different meaning depending on parameter 12 setting
ALARM CODE DESCRIPTION
Item
Code
Description
1
E1
Internal sensor warning.
2
HI
High temperature warning. Room temperature >55°C (>131°F)
3
LO
Low temperature warning. Room temperature <0°C (<32°F) or internal sensor opened.
4
E5
Dew point risk warning. Valves and fan are shut off when error is active.
8
E6
Filter alarm
9
E7
BI warning
P/N 24-11446-00018 Rev. B Issue Date: 11 2020
Parameter name
HTG-STG
BI-PLRT
OCC-OVRD
FAN-DELAY
ECM-RLY
Default
Function
00: One Heating Stage - Fan Coil
02
01: One Heating Stage - Floor Heating
02: Two heating stage
BI polarity:
01
00: Normally Close
01: Normally Open
Override the OCC-S value:
00: No Override
00
01: Occupied
02: Unoccupied
00
Fan off delay after valve closed, in seconds (0-99 s)
00: Disable
00
01: Enable