T9200
USER SETTING
PARAMETER SETTING
Press
and
button for 5 seconds at power off mode to get in parameter list. Press
the list and use
and
button to change the parameter value.
T9200-
T9200-
Code
TB21-1JS0
TF20-1JS0
■
■
04
■
■
05
■
■
06
■
■
07
■
08
■
09
■
10
■
■
11
■
■
12
■
■
13
■
■
16
■
■
17
■
■
18
■
■
20
P/N 24-11446-00018 Rev. B Issue Date: 11 2020
Parameter name
MUTE
OFFSET
UNOCC-CLG-SP
UNOCC-HTG-SP
SMPL-TM
PB
KI
BL-TIMER
PWR-F-RSTT
TIO2ESP-CTL
KEY-LOCK
TEMP-DISP
UNIT
SF-VERSION
to scroll forward and M button to scroll backward in
Default
Function
Enable/disable the beep when push touch button:
00
00: Disable
01: Enable
Offset to be compensate the room temperature:
0°C/0°F
Step: 0.5°C (1°F)
Range: -5~5°C (-9-9°F)
Cooling setpoint unoccupied mode.
26°C/
Not available for Boiler application
Step: 0.5°C (1°F)
79°F
Range: 22~32°C (72-90°F)
Heating setpoint unoccupied mode.
18°C/
Step: 0.5°C (1°F)
64°F
Range: 10~21°C (50-70°F)
Sample time,
10 s
PID parameter, only for PID
Range: 1~99 s
Proportion band,
5
PID parameter, only for PID
Range: 1~10
Integration parameter,
10
PID parameter, only for PID
Range: 0~99
Backlight timer
30
Range: 5~99S
Restart after power failure:
00: OFF
02
01: ON
02: Recovery
TIO2ESP control:
00: Automatic
00
01: Manual
For TIO2ESP application
Key lock function:
00: No lockout
01: Level 1 >Lock all keys
00
02: Level 2 >Lock the keys except Fan Speed and Temp Adjustment keys
03: Level 3 >Lock the ON/OFF and Clock keys
04: Level 4 >Lock the keys except ON/OFF key
UI display room temperature or set point:
00
00: Room Temperature
01: Setpoint
Unit selection:
00
00: IP
01: SI
Software version, read only
English