6.2 Panel Cutting Dimensions
Make holes in the panel according to the dimensions list below.
Also, ensure 10mm of space in upper and lower parts of the panel for mounting fixtures.
Horizontal format (If the vertical format is selected, the dimension must be rotated 90 degrees.)
6.3 Mounting Position
When mounting the GOT, the following clearances must be maintained from other structures and devices.
The below diagram represents a horizontal installation. (The same clearances must be maintained when
rotating the GOT 90 degrees clockwise for a vertical installation.)
Secure 50mm (1.97") or more of clearance on the left, right and bottom sides of the GOT from other
structures and devices.
Secure 80mm (3.15") or more on the top of the GOT for good ventilation.
If devices (such as a contactor) generating radiated noise or those generating heat are arranged around the
GOT, secure 100mm (3.94") or more of clearance from the back panel.
When using the CF card, secure a sufficient distance on the left side to allow installation and removal of the
CF card.
[Securing 100mm (3.94") or more is recommended.]
6 - 4
6.2 Panel Cutting Dimensions
+2
+0.08"
153
(6.03"
)
-0
-0
50mm
(1.97")
or more
To use the CF card, leave sufficient
distances for removal and installation
of the CF card.
10 (0.4")
or more
10 (0.4")
or more
Unit: mm (inch)
80mm (3.15") or more
50mm
(1.97")
or more
50mm (1.97") or more