Installation Recommendations; Examples Of Integration - Landis+Gyr ULTRAHEAT T450 Technical Description

Static heat and cooling meter t450 residential; local and district heating
Hide thumbs Also See for ULTRAHEAT T450:
Table of Contents

Advertisement

Installation

Installation recommendations

Examples of integration

Briefly press button 2 to display the current installation location. Depending
on the installation location,
To change the installation location, press button 1. The display changes.
Press button 2 briefly until "*" appears on the LCD.
To complete the parameterization, briefly press button 1 several times until
"
" appears on the LCD.
Press button 2 briefly to complete the change.
The change can be checked using the symbols (
If necessary, adjust the temperature sensors according to the installation
requirements.
During installation, make sure that water cannot enter into the calculator
during operation.
Inlet or outlet sections are not necessary but are recommended.
If you install the meter in the common return of two circuits, select an instal-
lation location with a minimum distance of 10 × DN from the T-piece.
The temperature sensor ends should reach at least into the middle of the
pipe cross-section.
Ball valve
Fig. 6: Installation with ball valve (recommended up to and including DN25)
Fig. 7: Installation for circulation with admixture; placement of temperature sensors
or
is displayed.
or
) on the LCD.
11/36