Installation Instructions

1 General information

The meter has left the factory in a technically safe condition.
Further technical support is provided by the manufacturer on
request. The meter's calibration-relevant security symbols must
not be damaged or removed. Otherwise, the warranty and
calibration validity of the meter will be invalidated.
Keep the packaging in a safe place so that you can transport
the meter in its original packaging after the calibration
validity has expired.
Lay all cables at a minimum distance of 500 mm from power
and high-frequency cables.
A relative humidity of < 93 % at 25°C is permissible (non-
condensing).
Avoid overpressure cavitation throughout the system, i.e. at
least 1 bar for qp and approx. 3 bar for qs (applies for
approx. 80 °C).
The control line must not be cut, shortened or extended.
In the case of a heat meter or combined heat/cooling
meter, the cold side installation location corresponds to the
return
and the warm side installation location
corresponds to the supply
In the case of a cooling meter
installation location corresponds to the return
cold side installation location to the supply

2 Safety instructions

Caution
The meters may only be used in building installations and
only for the applications described.
Caution
The local regulations (installation, etc.) must be observed.
Caution
The operating conditions on the nameplate must be
observed during use. Failure to comply with these
regulations can cause dangerous situations and voids all
claims arising from liability for defects as well as liability on
the basis of any expressly granted guarantees.
Caution
Comply with the requirements for circulation water (CEN /
TR 16911:2016).
Caution
The meter is only suitable for circulation water in heating
systems.
© Landis+Gyr
Ultrasonic Heat and Cooling Meter
ULTRAHEAT T450
ULTRACOLD T450
.
, the warm side
and the
.
Subject to change without prior notice
Caution
The meter is not suitable for drinking water.
Caution
Do not lift the metre on the calculator.
Caution
Pay attention to sharp edges on threads, flanges and the
measuring tube.
Caution
Only personnel trained in the installation and operation of
meters in heating/cooling systems may install and remove
the meter.
Caution
Only install or remove the meter on an unpressurised
system.
Caution
After installing the meter, check the leak tightness of the
system.
Caution
Breaking the safety marks relevant for calibration voids the
warranty and the validity of the calibration.
Caution
Avoid contact of the meter housing with silicone oils or
substances containing silicone oil.
Caution
Only clean the meter from the outside with a soft, slightly
moistened cloth. Do not use spirits or cleaning agents.
Warning
The meter must not be energised until it has been fully
assembled. Otherwise there is a risk of electric shock on
the terminals. A defective or obviously damaged device
must be disconnected from the power supply immediately
and replaced.
Warning
The meter is valid for disposal as waste electronic
equipment within the meaning of the European Directive
2012/19/EU (WEEE) and must not be disposed of as
household waste. The corresponding national and legal
regulations must be observed and the device must be
disposed of via the channels provided for this purpose. The
local and currently valid legislation must be observed.
3221101002_a
07.02.2020
Translation
T450
07.02.2020
1

Advertisement

Table of Contents
loading
Need help?

Need help?

Do you have a question about the ULTRAHEAT T450 and is the answer not in the manual?

Questions and answers

Summary of Contents for Landis+Gyr ULTRAHEAT T450

  • Page 1 3221101002_a Installation Instructions Ultrasonic Heat and Cooling Meter 07.02.2020 ULTRAHEAT T450 Translation ULTRACOLD T450 T450 1 General information Caution The meter has left the factory in a technically safe condition. The meter is not suitable for drinking water. Further technical support is provided by the manufacturer on request.
  • Page 2 If you install the meter as a cooling meter, follow the corresponding instructions. Recommendation: If you install several meters, the same installation conditions should apply to all meters. © Landis+Gyr Subject to change without prior notice 07.02.2020...
  • Page 3 The temperature sensor ends should reach at least into the temperature sensor. This allows you to immerse the temperature middle of the pipe cross-section. sensor directly in an installation piece or a ball valve, for example. © Landis+Gyr Subject to change without prior notice 07.02.2020...
  • Page 4 The ambient temperature of the calculator must not exceed 55 °C. Avoid direct sunlight. For water temperatures between 10 °C and 90 °C, you can install the calculator on the volume measuring unit or on the wall. © Landis+Gyr Subject to change without prior notice 07.02.2020...
  • Page 5 7 Communication modules Note Observe the necessary ESD protection measures when installing modules. Figure 10: Battery compartment Number Description User protection Battery compartment cover screw Battery compartment cover © Landis+Gyr Subject to change without prior notice 07.02.2020...
  • Page 6 • Gently push the module in. • Strip both cables as shown in the illustration. Depending on the design of the housing, please also observe the following points: © Landis+Gyr Subject to change without prior notice 07.02.2020...
  • Page 7 (status at volume meter correspond to delivery) the flow direction of the system. If the directions do not match, rotate the volume meter 180°. © Landis+Gyr Subject to change without prior notice 07.02.2020...
  • Page 8 Error in internal Change the device. memory The measurements of the meter may no longer be used for legally calibrated billing. Landis+Gyr GmbH Humboldstrasse 64 90459 Nuremberg Germany © Landis+Gyr Subject to change without prior notice 07.02.2020...