Sun Microsystems Sun Fire T1000 Site Planning Manual

Sun Microsystems Sun Fire T1000 Site Planning Manual

Hide thumbs Also See for Sun Fire T1000:

Advertisement

Quick Links

Sun Fire
T1000 Server
Site Planning Guide
Sun Microsystems, Inc.
www.sun.com
Part No. 819-3749-11
July 2006, Revision A
Submit comments about this document at:
http://www.sun.com/hwdocs/feedback

Advertisement

Table of Contents
loading
Need help?

Need help?

Do you have a question about the Sun Fire T1000 and is the answer not in the manual?

Questions and answers

Subscribe to Our Youtube Channel

Summary of Contents for Sun Microsystems Sun Fire T1000

  • Page 1 Sun Fire T1000 Server ™ Site Planning Guide Sun Microsystems, Inc. www.sun.com Part No. 819-3749-11 July 2006, Revision A Submit comments about this document at: http://www.sun.com/hwdocs/feedback...
  • Page 2 Copyright 2006 Sun Microsystems, Inc., 4150 Network Circle, Santa Clara, Californie 95054, Etats-Unis. Tous droits réservés. Sun Microsystems, Inc. a les droits de propriété intellectuels relatants à la technologie qui est décrit dans ce document. En particulier, et sans la limitation, ces droits de propriété...
  • Page 3: Physical Dimensions

    This guide provides the specifications and site requirements you need when planning the installation of the Sun Fire™ T1000 server. For safety and compliance information, refer to the Sun Fire T1000 Server Safety and Compliance Manual and the Important Safety Information for Sun Hardware Systems document that came with your system.
  • Page 4: Clearance For Service Access

    Clearance, front of system 36 in (91 cm) Clearance, rear of system 36 in (91 cm) Environmental Specifications These are the environmental specifications for the Sun Fire T1000 server. Description Specification Operating Temperature: • Sea level to 3000 ft (900m) •...
  • Page 5: Power Source Requirements

    Power Source Requirements The Sun Fire T1000 server has an autoranging power supply. Description Specification Operating input voltage range 100 to 240 VAC, 50-60 Hz (Input voltage tolerance ± 10%) Maximum operating input current 2.2 A at 100 to 120 VAC 1.1 A at 200 to 240 VAC...
  • Page 6: Agency Compliance Specifications

    Agency Compliance Specifications The Sun Fire T1000 server complies with the following specifications. Category Relevant Standards Safety UL/CSA-60950-1, EN60950-1, IEC60950-1 CB Scheme with all country deviations, IEC825-1, 2, CFR21 part 1040, CNS14336, GB4943 RFI/EMI EN55022 Class A 47 CFR 15B Class A...
  • Page 7: General Site Preparation Notes

    Provide an operating time buffer in the event of environmental control system ■ failure Help avoid failures caused by the intermittent interference from static discharges ■ that occur when relative humidity is too low Sun Fire T1000 Server Site Planning Guide...
  • Page 8: Airflow Considerations

    Care should be taken to prevent recirculation of exhaust air within a rack or ■ cabinet. Cables should be managed to minimize interfering with the server exhaust vent. ■ Air temperature rise through the system is approximately 59˚F (15˚C). ■ Sun Fire T1000 Server Site Planning Guide • July 2006...