Exhaust duct

•­ The­exhaust­duct­must­be­smooth­on­the­inside­(low­air­resistance).­
•­ The­exhaust­duct­must­lead­to­the­outdoors.­
•­ The­exhaust­duct­must­lead­clear­of­the­building­as­condensation­may­
cause frost damage to the building.
•­ The­exhaust­duct­must­be­protected­against­rain­and­foreign­objects.­
•­ The­exhaust­duct­must­have­gentle­bends.
8
•­ The­exhaust­duct­must­not­be­a­shared­duct­between­dryers­and­appli-
ances using gas or other fuels as their energy source.
When several dryers share an exhaust duct
•­ The­exhaust­duct­diameter­must­increase­after­each­dryer.
9
The table below shows the exhaust duct diameter and the necessary
fresh-air inlet area.
Note! It is recommended that each dryer is connected to a separate
exhaust duct.
The evacuation pipe diameter must not be reduced.
No. of dryers
1
Exhaust
m
/h
260
3
d
ø mm
100
Fresh air inlet
cm
400
2
Exhaust duct
length 0-6 m d
ø
100
** Exhaust duct
length 6-50 m d ø
160
If the exhaust duct lenght exceeds 6 m the diameter must be increased.
**
Installation
2
3
4
520
780
1040
100
100
100
800
1200
1600
160
200
250
200
250
350