6.3 Exhaust duct

• Only rigid or flexible metal duct should be used for exhausting.
• Plastic ducting is not to be used.
• Recommended material for exhaust is galvanized steel.
• The duct is not to be assembled with screws of other fastening means that extend into the duct and catch lint.
• The exhaust air should not be vented into a wall, a ceiling, or a concealed space of building.
• The exhaust duct must lead clear of the building as condensation may cause frost damage to the building.
• The exhaust duct must lead to the outdoors.
• The exhaust duct must be placed in such a way that it is protected on the outside.
• The exhaust duct must be smooth on the inside (low air resistance).
• The exhaust duct must have gentle bends.

6.4 Shared exhaust duct

It is recommended that each machine is connected to a separate exhaust duct.
When several machines shall use the same exhaust duct the exhaust duct must increase after each machine.
Number of machines
Exhaust duct
⌀ mm
Recommended area
of fresh air intake
Minimum area of
fresh air intake
The exhaust duct diameter must not be reduced.
Installation manual
1
2
100
160
m
2
0.04
0.1
0.16
m
2
0.011
0.022
0.033
3
4
5
200
200
250
0.16
0.25
0.044
0.055
6
7
8
250
315
315
0.25
0.39
0.39
0.066
0.077
0.088
fig.W00198
9
10
315
315
0.39
0.39
0.099
0.11