3. Important Safety Instructions

This manual contains important instructions that should be followed during the installation and maintenance
of the UPS and its batteries.
The T1000 Series UPS is a modular single-phase double conversion system. Each of the rackmount
modules is 3U (Three Standard Rack Units) high.
UPS systems are not equipped with an over-current protection device nor an output disconnect for the AC
output. Circuit breakers should be provided by the user between the UPS Input and utility power, and the
UPS output and the load input. This device should be rated as follows:
The nominal battery voltages for these models is as follows:
Servicing the batteries should only be performed by a qualified factory authorized representative who is
knowledgeable about batteries and the required precautions. Keep unauthorized personnel away from
batteries. To arrange for battery replacement, contact Toshiba Customer Support Center.
1.
Turn off, lockout, and tagout all equipment before connecting the power wiring to the equipment or
when performing maintenance.
2.
The maximum ambient operating temperature is 104 °F (40 °C). UPS will go to Bypass when it
overheats.
3.
Access panels should only be removed by authorized Toshiba field Service personnel.
4.
UPS servicing should be performed by qualified Toshiba representatives only.
5.
Battery servicing should be performed by qualified Toshiba representatives only.
6.
Contact your Toshiba authorized service center for battery replacement.
T1000 Series UPS Installation and Operation Manual – 91074-002
240/208 VAC RATING*
Input Breaker
240 V / 208 V
Output Breaker
240V / 208V
* Ratings are for a 80% rated device.
UNIT
BATTERY VOLTAGE
6 kVA
(1 string of 18 x 12V batteries)
6 kVA
40 A
40 A
216 Vdc (Nominal)