7. Wiring the System

7.1 Layout - Power Module

1
2
INPUT MCCB1
REMOTEYE
208V/240VAC 30A
5
6
No. Label
1
INPUT MCCB1
208V/240VDC 30A
2
REMOTEYE
3
REM. CONTACTS
4
OUTPUT L6-30R
208/240VAC 25A
5
EXT. BATTERY
6
INPUT L N G
7
REM. STOP
8
EPO 240V
9
OUTPUT L N G
FIGURE 7-2: POWER MODULE -
HARDWIRED CONFIGURATION
(P/N T1P0A6000GVG,
T1P0A6000GVGR3)
3-Post Input Terminal Block, and
one each 3-Post Output Terminal
Block and NEMA L6-30R outlet.
FIGURE 7-3: POWER MODULE WITH
6-50P LINECORD (-L1) OPTION
(P/N T1P0A6000GVGL1,
T1P0A6000GVGR3L1)
Input Power Cord #10-3SO 6-50P
and two each NEMA L6-30R outlets.
16
3
USE COPPER 75°C MIN.
CONDUCTORS ONLY
EPO 240V
8
SEE INSTRUCTION MANUAL FOR WIRING
TERMINATION AND TIGHTENING TORQUE
REM. STOP
7
FIGURE 7-1: POWER MODULE BACK PANEL LAYOUT
TABLE 7-1: POWER MODULE BACK PANEL LAYOUT
Function
Main On/Off circuit breaker.
Cover plate for RemotEye
Dry contacts DB9 connector.
Output receptacle for L6-30P cord (alternate output for 208/240 only)
External Battery Module Anderson receptacle.
Hardwire input terminals Line, Neutral, and Ground.
Remote Stop Contacts. (TB4) (10 VDC)
Remote Emergency Power Off (EPO) Contacts. (TB3) (240/208 VAC)
Hardwire output terminals Line, Neutral, and Ground.
T1000 Series UPS Installation and Operation Manual – 91074-002
circuit card slot.
®
EPO 240V
REM. STOP
EPO 240V
REM. STOP
4
OUTPUT L6-30R
208/240VAC 25A
9
(TB1)
(TB2)