10. UPS Operation

10.1

Initial Startup

The following parameters need to be input before connecting the load to the UPS. The most convenient
access is to use the Quick Config menu using the example in Section 9.4.
See Section 9 for control panel explanations and display navigation.
1.
Ensure no loads are connected to the UPS outlets.
2.
Apply power to the T1000 UPS System. Switch on MCCB1. The ONLINE/FAULT LED will briefly
illuminate, then turn off.
3.
In Bypass, the UPS ONLINE/FAULT LED should be Off, and the AC INPUT LED a steady Green.
4.
Access the MENU, open QUICK CONFIG, and ensure the following parameters are set properly. When
changing/entering a new value, be sure to press the ENTER/MENU push button and verify the screen
returns a Success message.
Input Voltage - Select the input voltage to the UPS.
Path: MENU > QUICK CONFIG > Rated Vin > Rated Vin: xxxV
Output Voltage - Select the output voltage to the Load.
Path: MENU > QUICK CONFIG > Rated Vout > Rated Vout: xxxV
Vout Adjust - Increase/decrease the output voltage slightly to compensate for line losses.
Default - 0V
Path: MENU > QUICK CONFIG > Vout Adjust > Vout Adjust: xxV
Battery Installation Date - Set during factory testing. Reset when battery modules are replaced.
Path: MENU > QUICK CONFIG > Batt Ins Date > Batt Ins Date: mm/dd/yyyy
UPS Date - Current Date. Set at the factory and backed up by an internal battery. Only change
when necessary.
Path: MENU > QUICK CONFIG > UPS Date > UPS Date: ddd mm/dd/yyyy
UPS Time - Current time. Set at the factory for US Central Standard Time and backed up by an
internal battery. Only change when necessary.
Path: MENU > QUICK CONFIG > UPS Time > UPS Time: hh:mm AM/PM
Enable Batt Test - Enable or disable battery testing. Default - Enable.
Path: MENU > QUICK CONFIG > En Batt Test* > En Batt Test Sup* > En Batt Test*: Enable/
Disable
5.
Press the ESC/MUTE push button until the STATUS screen is displayed.
6.
Leave the Power Module in bypass mode to allow the battery module(s) to charge for 24 hrs. before
placing the Power Module online.
ALLOW 24 HOURS FOR THE POWER MODULE TO RECHARGE THE
BATTERY MODULE(S) BEFORE PLACING THE UPS IN SERVICE.
7.
Place the UPS online by pressing and momentarily holding the RUN/STOP push button. The ONLINE/
FAULT LED should glow steady GREEN.
NOTE: Bypass is automatically disabled if the Rated Vin and Rated Vout are different.
26
T1000 Series UPS Installation and Operation Manual – 91074-002