Spectra T120 Robotics Assembly Replacement Instructions This document provides instructions on how to replace a robotic assembly ® in the Spectra T120 library. Illustrations Whenever possible, the illustrations in this guide show the components from the front of the library, either looking at the front of the library or in through the front door. When it is helpful, the E/E port— located in the front door—is referenced as a “landmark” of the component location. Model Variations The model you are installing may vary slightly from the illustrations in this document; however, the steps in the procedure are the same regardless of the replacement model. If your assembly includes a T8 Torx L‐key and screw, use them as noted. Time Estimate The procedure takes approximately 60 minutes. REPARE FOR AINTENANCE Ensure ESD Protection The repair environment for the library must be free of conditions that could cause electrostatic discharge (ESD). To protect the library from ESD, follow these procedures when repairing or testing the library: Place a static protection mat on the work surface used while removing and installing library components. Use a 1‐megohm resistor to ground the static protection mat. Wear a static protection wrist band or grounding foot strap whenever ...
Spectra T120 Robotics Assembly Replacement Instructions Prepare for Maintenance Gather Tools and Supplies When unpacking the new robotics assembly, note both the packaging materials Caution and the packing method. After you install the new assembly, package the old assembly using the same method and packaging. Return the properly packaged assembly to Spectra Logic for inspection.
Spectra T120 Robotics Assembly Replacement Instructions Prepare for Maintenance 2. Use your backup software to move any cartridges that are currently in drives back to their storage locations. If you cannot use your backup software, then move the cartridges as described in the Spectra T120 Library User Guide. Pause PostScan, if it is running, as described in the Spectra T120 Library User Guide. Any tapes currently being scanned are returned to their storage locations. 4. Look through the library front door to verify that the robot is not moving. It should be parked at the bottom of the library. Power Off the Library Follow these steps to power off the library. You need access to both the front and back of the library. 1. Front—Press the front panel power button until the button’s LED starts to flash. Wait for the power‐off sequence to complete, which allows the applications to shut down gracefully. The power‐off sequence is complete when the front panel user interface is no longer illuminated. Library Front Library Back Front panel Power button user interface...
Page 6
Spectra T120 Robotics Assembly Replacement Instructions Prepare for Maintenance Identify the Robotics Assembly Components Figure 2 shows the robotics assembly components. Library Front (door removed for clarity) Upper HAX Upper HAX (Horizontal guide rails Axis) drive belt Front panel user interface Upper HAX rod E/E port...
Page 7
Spectra T120 Robotics Assembly Replacement Instructions Remove the Robotics Assembly EMOVE THE OBOTICS SSEMBLY This section describes how to remove the robotics assembly from the library. Preparing to Remove the Assembly 1. Disconnect the motor control cable. a. Squeeze the retaining clip in the center of the connector, which is located on the back side of the connector (interior of library). b. Gently pull the motor control cable upward to disconnect it from the motor control board at the front of the library. E/E port Library Front Motor control cable connector Figure 3 Disconnect the motor control cable.
Page 8
Spectra T120 Robotics Assembly Replacement Instructions Remove the Robotics Assembly 2. Turn the HAX (horizontal axis) belt pulley counter‐clockwise to move the robotics assembly forward. Stop the assembly when it is approximately three‐quarters of the way to the front of the library. belt pulley Library Right-Front Figure 4 Turning the HAX belt pulley. Do not move the robotics assembly by physically pulling it forward; doing so may Caution cause additional damage.
Page 9
Spectra T120 Robotics Assembly Replacement Instructions Remove the Robotics Assembly 4. Locate the screw at the top of the library securing the upper HAX belt bracket to the upper HAX bracket at the top of the VAX column. Library Front Remove E/E port the screw Detail showing screw removed Figure 6 Remove the HAX belt bracket screw at the top of the library. 5. Use a #1 Phillips screwdriver to remove the screw (or a T‐9 Torx driver ...
Page 10
Spectra T120 Robotics Assembly Replacement Instructions Remove the Robotics Assembly 6. Locate the HAX rod coupler, which attaches the lower HAX rod to the upper HAX rod. Loosen all 4 Allen screws. Slide coupler up. Tighten 1 screw. Figure 7 The HAX rod coupler. 7. Use a 3/32‐inch Allen wrench to loosen, but do not remove, the four Allen screws on the coupler so that it moves freely. 8. Slide the coupler several inches upward on the upper HAX rod and tighten one screw to hold the coupler temporarily in place. The lower HAX rod is removed with the robotics assembly, and the coupler is used to secure the two rod sections together when the new assembly is installed. 9. Carefully rotate the VAX column counter‐clockwise so that the back of ...
Page 11
Spectra T120 Robotics Assembly Replacement Instructions Remove the Robotics Assembly Removing the Robotics Assembly 1. Using a #1 Phillips screwdriver, loosen the three captive screws that attach the robotics assembly base to the library chassis. The captive screws consist of one thumb screw and two quarter‐turn screws. Library Front Screws (3x) Figure 9 The three chassis screws. 2. Gently pull the base forward while pressing down on the ribbon cable until the cable is clear of the library. Make sure the motor control cable does not catch on the assembly base as you remove it. It may be helpful to have another person hold the motor control cable out of the way. To avoid damaging the cables, protect both the motor control cable and the Caution ribbon cable when you remove the robotics assembly.
Page 12
Spectra T120 Robotics Assembly Replacement Instructions Disassemble the Failed Robot 3. While grasping both sides of the assembly, slide it completely out of the library chassis. The robotics assembly can be awkward to handle. Use caution when moving the Caution assembly to avoid damage. Use two people if necessary. 4. Place the assembly on a flat, sturdy work surface. ISASSEMBLE THE...
Page 13
Spectra T120 Robotics Assembly Replacement Instructions Disassemble the Failed Robot 2. Attach a small binder clip to the metal edge of the VAX column to secure the robot in place, so that it remains at the top of the VAX column. Binder clip VAX column Figure 12 The robot clipped in place. 3. Detach the ribbon cable or cables. Old Style Robot—The older models of the robotic assembly have a single dual‐row ribbon cable with one connector. Press down on the locking tab and pull the cable out of the connector. Figure 13 Disconnect the cable. March 2015 Robotic Assembly Replacement—Spectra T120 Library...
Page 14
Spectra T120 Robotics Assembly Replacement Instructions Disassemble the Failed Robot New Style Robot—The newer models of the robotic assembly have two ribbon cables. Pull the cable plugs away from the connector to release the cable, then pull the cable out of the connector. Repeat for the second cable. Release cable plugs Disconnect cables Figure 14 Disconnect the ribbon cables. 4. Use a #2 Phillips screwdriver to remove the two screws attaching the lower HAX belt bracket to the robotics assembly. HAX belt bracket Bracket screws Figure 15 Remove the lower HAX belt bracket screws.
Page 15
Spectra T120 Robotics Assembly Replacement Instructions Assemble the Replacement Robot 6. Use a #1 Phillips screwdriver to remove the four bearing screws attaching the assembly to the first of its two HAX bearing blocks. Bearing screws Bearing screws (hidden) Figure 16 Remove the screws securing the assembly to the base. 7. Rotate the VAX column to expose the second set of four bearing screws (hidden in Figure 16), then remove them using a #1 Phillips screwdriver. 8. Carefully lift the robotics assembly vertically off the HAX bearing blocks, and place the assembly on its side. Remove the small binder clip attached in Step 2 on page 13. Carefully ...
Page 16
Spectra T120 Robotics Assembly Replacement Instructions Assemble the Replacement Robot Attaching the Robot to the Base 1. Locate the two HAX bearing blocks on the replacement assembly base, and space the blocks approximately 5 inches (12.7 cm) apart. Library Back HAX bearing blocks Library Front Figure 17 The two HAX bearing blocks on the assembly base. 2. Carefully place the robotics assembly onto the base, on top of the two HAX bearing blocks, so that the assembly is oriented as shown.
Page 17
Spectra T120 Robotics Assembly Replacement Instructions Assemble the Replacement Robot 4. Install the bearing screws. a. Use a #1 Phillips screwdriver to loosely install the four accessible bearing screws. Looking straight down on the robotics assembly. Bearing screws Bearing screws (hidden) Figure 19 Attach the screws to secure the assembly to the base. b. Rotate the VAX column to reveal the four screw holes on the ...
Page 18
Spectra T120 Robotics Assembly Replacement Instructions Assemble the Replacement Robot Attaching the Bracket and Cables 1. Use a #2 Phillips screwdriver to secure the two screws attaching the lower HAX belt bracket to the robotics assembly base. Older style robots attach to the lower HAX belt bracket in a Note: different orientation. Figure 21 Attaching the lower HAX belt bracket. 2. Using the HAX belt pulley, move the robotics assembly to the front of the assembly base (see Figure 11 on page 12). 3. Attach the ribbon cable. Old Style Robot—Route the ribbon cable to make sure it is not bent, then seat the cable in the cable connector until the tab locks the cable in place.
Page 19
Spectra T120 Robotics Assembly Replacement Instructions Installing the Assembly in the Library 4. Examine the ribbon cable and make sure the cable comes straight out of the cable bracket, and is not curled over the bracket. Ribbon cable Cable bracket Figure 23 Correctly routed ribbon cable. Remove the small binder clip used in Step 3 on page 15. The robot mechanism gradually descends. NSTALLING THE SSEMBLY IN THE IBRARY Attaching the Robotics Assembly to the Chassis 1.
Page 20
Spectra T120 Robotics Assembly Replacement Instructions Installing the Assembly in the Library 2. Before installing the replacement robotic assembly, note the alignment pins inside the library and the matching pin guides on the base of the assembly. Align the pins with the spaces in the back of the robotic assembly base. Align these two surfaces with the two pins shown. The surface on Back this side of the base plate is under a pulley assembly.
Page 21
Spectra T120 Robotics Assembly Replacement Instructions Installing the Assembly in the Library 4. Slide the assembly part way into the library. Use one hand to press down on the ribbon cable so that it does not catch on the E/E plate. Hold the motor control cable so it does not catch on the assembly base. It may be helpful to have another person hold the motor control cable. To avoid damaging the cables, protect both the motor control cable and the Caution ribbon cable when you remove the robotics assembly.
Page 22
Spectra T120 Robotics Assembly Replacement Instructions Installing the Assembly in the Library 7. Slide the assembly fully into the library. 8. Make sure that the front of the assembly base is flush with the front of the library chassis. You may need to push the assembly in with substantial force to seat it fully. Assembly base Chassis Library Front (looking down inside front) Figure 29 Fully seated assembly. 9. Using a #1 Phillips screwdriver, secure the assembly to the library by installing the captive three screws. The captive screws consist of one thumb screw and two quarter‐turn screws. Library Front Screws (3x) Figure 30 The three chassis screws.
Page 23
Spectra T120 Robotics Assembly Replacement Instructions Installing the Assembly in the Library Aligning the VAX Column Follow these steps to align the VAX column: 1. By hand, rotate the VAX column clockwise so the back of the VAX column is facing toward the left side of the library. The VAX column rotated completely to the left. E/E port Figure 31 Rotating the VAX column. 2. Locate the upper HAX belt bracket, then rotate the HAX belt pulley until the holes in the upper HAX belt bracket align with the holes in the upper HAX bracket at the top of the VAX column.
Page 24
Spectra T120 Robotics Assembly Replacement Instructions Installing the Assembly in the Library 3. Attach the upper HAX belt bracket to the upper HAX bracket. If the replacement robotics assembly includes a Torx screw, use a T‐9 Torx driver to install the supplied Torx screw. If the replacement robotics assembly does not include a Torx screw, use a #1 Phillips screwdriver and the screw removed in Step 5 on page Library Front Bracket screw HAX rod Figure 33 The HAX belt bracket at the top of the library.
Page 25
Spectra T120 Robotics Assembly Replacement Instructions Installing the Assembly in the Library 5. Rotate the HAX belt pulley to move the robotics assembly to the front of the library. It must be positioned firmly against the hard stop. Upper HAX rod (coupler removed) Lower HAX rod Hard stop HAX belt pulley Library Front (looking down inside front) Figure 34 The hard stop position.
Page 26
Spectra T120 Robotics Assembly Replacement Instructions Installing the Assembly in the Library 7. With the shipping screw in the alignment position and the robotics assembly pressed firmly against the hard stop, position the coupler. a. Use a 3/32‐inch Allen wrench to loosen the single screw holding the coupler on the top HAX rod. b. Position the coupler so that: The top two screws secure the top portion of the coupler to the upper HAX rod. The bottom two screws secure the bottom portion of the coupler to the lower HAX rod. Note: When aligned correctly, a business card fits all the way through the center slot in the coupler, and the gap between the two HAX rods. Upper HAX rod Align so the top and bottom rods...
Spectra T120 Robotics Assembly Replacement Instructions Complete the Procedure 10. Connect the motor control cable. a. Rotate the HAX belt pulley, moving the VAX column back a few inches, to provide access to the motor control cable connector. b. Connect the cable by seating the cable in the cable connector until the tab locks the cable in place. Library Front Motor control cable connector Figure 37 Reconnect the motor control cable. OMPLETE THE ROCEDURE Follow these steps in this section to complete the procedure. Powering on the Library 1. Close the library front door and lock it with the library key.
Page 28
Spectra T120 Robotics Assembly Replacement Instructions Complete the Procedure Testing the Robotics Assembly 1. Log in to the library as a user with superuser or administrator privileges. 2. Select Maintenance > Diagnostics. The Diagnostics screen displays. ® Note: The BlueScale interface changes as new features are added or other modifications are made between firmware revisions. Therefore, the user interface screen on your library may differ from the screen shown in this document. Figure 38 The Diagnostics screen. 3. Select All Motion Basic Tests. The Diagnostics screen refreshes to show details of the selected diagnostic.
Spectra T120 Robotics Assembly Replacement Instructions Return the Component ETURN THE OMPONENT Return Guidelines Unless Spectra Logic Technical Support informs you otherwise, return the defective component to Spectra Logic as described in the following section. If Spectra Logic Technical Support informs you that the component does not need to be returned, dispose of it following your company guidelines. Return Procedures After you complete the replacement procedure, return the defective component using ALL of the packaging material shipped with the replacement component. Severe damage can occur if the component is not packaged correctly, and you may Caution be invoiced if it is received with damage due to improper or insufficient packaging.
Page 30
Spectra T120 Robotics Assembly Replacement Instructions Get Help from Spectra Logic Step Description a. Wrap the VAX robotics assembly in the anti‐static bag that you removed Base from the replacement assembly in packaging robotics assembly. b. Place the packaging and components into the box in the order shown here. Middle support Note: Refer to Gather Tools and Supplies on page 4 for identification of robotics components.