Exhaust duct
It is recommended that each dryer be
connected separately to a smooth air outlet pipe
with the lowest possible friction.
If more than one dryer is connected to the same
Fig
3
outlet pipe, the pipe diameter must be
increased after each dryer, just as all dryers
must be equipped with a back draft damper to
prevent humid air from running back into dryers
that are not in operation.
The pipe must end outside in the open. The
outlet must be protected against rain, foreign
objects and prevailing winds.
Note! In cold areas, condensation may cause
frost damage to the building.
Gentle bends
To keep the air fl owing, ensure proper dryer
Fig
operation, and minimise lint buildup in the
4
exhaust system, never connect ducts at right
angles, always use gentle bends.
Service organisation/dealer
If you have questions relating to the design of
the exhaust system, please contact your local
dealer or service organisation.
No. of dryers
1
2
3
4
Installation
Outlet
d
3
m
/h
mm
290
Ø125
440
Ø125
660
Ø125
880
Ø125
3
4
Fresh-air intake
Pipe length 0-70 m
2
cm
400
800
1200
1600
d
Ø125
Ø160
Ø200
Ø250