Daikin T9000 Installation And Maintenance Manual page 5

Wireless 24vac thermostat remote control node (rcn)
Table of Contents

Advertisement

Figure 3: Adhesive tape used to secure the RCN box
NOTICE
It is recommended that the terminal block on the RCN control
module be removed when making terminal connections, to avoid
excessive handling of the static sensitive RCN control module.
5 . Remove the green terminal block from the RCN control
module, by pulling up & away from the control module.
Figure 4: Remove terminal block from RCN control module
IM 1119-1
6 . Wire all appropriate terminals on the removed Remote Control
Node terminal block (RCN), using appropriate lengths of field-
supplied low voltage wiring. Make sure to follow all national
and local code requirements when routing low voltage control
wires.
7 . Feed the stripped leads of the thermostat low-voltage wires
through the bushing of the RCN housing, to connect to the
unit control board or terminal strip/block.
Figure 5: Feed stripped wire leads through bushing on the
RCN housing
5
www.DaikinApplied.com