RCN Application – Configuration
Remote control nodes are factory-programmed to default
settings. Settings can be changed for special applications by
following the directions below. While programming, refer to
Figure
17 and the "RCN Configuration Table for All WSHP
Units" on page 13.
1 . To enter the setup mode press and hold PB3 until the LED
indicator lamps flash alternately.
2 . D4 will flash once indicating, "Table 1 - Control Mode"
on page
13
and
Figure
17; followed by D3 flashing 1
time, indicating the configuration that is active (1 flash for
WSHP).
3 . Pressing PB2 will advance the configuration value by 1 until
the D3 flash count corresponds to the desired configuration
in the "RCN Configuration Table for All WSHP Units" on
page
13.
4 . Pressing PB1 advances the table value until the D4 flash
count corresponds to the desired table (1-6).
5 . At any time in the set up process, PB3 can be pressed to
return to normal operation, saving any changes made.
IM 1119-1
Figure 17: RCN LED Indicator Lamp Locations
12
www.DaikinApplied.com