Comet T5410 Instruction Manual

Comet T5410 Instruction Manual

Programmable transmitter of temperature with rs232 / rs485 serial output. programmable transmitter of atmospheric pressure and temperature.

Advertisement

Quick Links

Programmable transmitter of temperature
T0310, T0410
Programmable transmitter of atmospheric pressure
and temperature
T5410
with RS232 / RS485 serial output
Instruction Manual
© Copyright: COMET SYSTEM, Ltd.
It is prohibited to copy and make any changes in this manual, without explicit agreement
of company COMET SYSTEM, Ltd. All rights reserved.
COMET SYSTEM, Ltd. makes constant development and improvement of their products.
Manufacturer reserves the right to make technical changes to the device without previous notice.
Misprints reserved.
Manufacturer is not responsible for damages caused by using the device in conflict with this
manual.
To damages caused by using the device in conflict with this manual cannot be provide free repairs
during the warranty period.
Read carefully instruction manual before the first device connection.
Contact address of this device's producer:
COMET SYSTEM, s.r.o.
Bezrucova 2901
756 61 Roznov pod Radhostem
Czech Republic
www.cometsystem.com

Advertisement

Table of Contents
loading
Need help?

Need help?

Do you have a question about the T5410 and is the answer not in the manual?

Questions and answers

Summary of Contents for Comet T5410

  • Page 1 It is prohibited to copy and make any changes in this manual, without explicit agreement of company COMET SYSTEM, Ltd. All rights reserved. COMET SYSTEM, Ltd. makes constant development and improvement of their products. Manufacturer reserves the right to make technical changes to the device without previous notice.
  • Page 2: Device Setting From The Manufacturer

    ✓ ✓ T5410 RS485 Device is designed for measurement of ambient temperature at °C or °F, device T5410 support atmospheric pressure measurement at hPa, PSI, inHg, mBar, oz/in , mmHg, inH O and kPa too. It is possible to set pressure correction for altitude (offset). Device setting is provided by user’s software, see latter.
  • Page 3: Device Installation

    1200m. The cable must be located at indoor rooms. Nominal cable impedance should be 100 Ω, loop resistance max. 240 Ω, cable capacity max. 65 pF/m. Outside diameter of the cable for T0410 and T5410 connection must be from 3 to 6.5 mm. Suitable cable is e.g. SYKFY 2x2x0.5 mm , where one wire pair serves for device powering and the other pair for communication link.
  • Page 4 Dimensions – T0410, T5410 Transmitter with RS485 Dimensions – T0310L, T0410L, T5410L Connection: see Appendix B IE-SNC-T03(4)10+T5410-06...
  • Page 5: Typical Application Wiring, Connection Of Terminals

    Typical application wiring, connection of terminals T0310 – power from communication port T0310 – power from external voltage source T0410, T5410 – RS485 IE-SNC-T03(4)10+T5410-06...
  • Page 6: Info Mode

    15 s, device automatically returns to measuring cycle. Setting of pressure correction for altitude For device T5410 only! If there is necessary to read value of atmospheric pressure corrected with respect to altitude, it is possible to set corresponding pressure offset for this altitude. It is possible to do it with Users software.
  • Page 7 4150 BIN16 device Lo Version of 0x3001 12289 BIN16 Firmware Hi Version of 0x3002 12290 BIN16 Firmware Lo Addition for device T5410 - with atmospheric pressure measurement Variable Unit* Address[hex] Address[dec] Format Size Status Int*10 Int*1000 inHg Int*100 mBar Int*10...
  • Page 8 “dEF” message blinking at LCD display. Six seconds later message “dEF” stays shown, it means manufacturer setting of communication protocol is done. For communication with device T5410 which measure more than one value, there is necessary to add at the end of command, number of communication channel, where the measured value is mapped.
  • Page 9: Error States Of The Device

    There is a reading „Err4“ on LCD display. It is internal device error during pressure sensor initialization. Under this condition device does NOT measure atmospheric pressure. Value read from device is -999.9. Pressure sensor is probably damaged. It is a serious error, contact distributor of the device. IE-SNC-T03(4)10+T5410-06...
  • Page 10: Readings On Lcd Display

    256 (1/8 Unit Receiver Load) Measuring parameters: Ambient temperature (RTD sensor Pt1000/3850ppm): -30 to +80 °C Measuring range: Resolution of display: 0.1 °C ± 0.4 °C Accuracy: Atmospheric pressure (T5410 only): Unit hPa, mBar mmHg inHg oz/in Range 8.70 450.0...
  • Page 11: End Of Operation

    Do not use the device in an explosive environment. Storing conditions: temperature -30 to +80 °C, humidity 0 to 100 %RH without condensation Dimensions: see dimensional drawings Weight: approximately T0310(L) 220 g, T0410(L) 140 g, T5410(L) 140 g Material of the case: ASA End of operation...
  • Page 12 RS485, 0V connect to pin 5 and link RS485 connect across pin 3 A(+) and pin 4 B(-). Time out setting is performed by connecting the corresponding pins of connector marked RS485 (for more information see the operation manual for ELO E06D). Appendix B IE-SNC-T03(4)10+T5410-06...

This manual is also suitable for:

T0410T0310