User Guide
EM-PMI540-T2000
Storage, installation and maintenance checklists
Electric machine and customer information
Customer:
Customer reference:
Service reference:
Installation checklist
Approval
General
Electric machine type is correct
Electric machine is
undamaged
Insulation resistance check
>150MΩ
(Reference value of 150 MΩ
should not be exceeded at
reference ambient
temperature 25°C (measured
with 500 V
/ 1 min
DC
Megger))
Environmental conditions as
specified (see data sheet)
Mechanical installation
Supporting structure as required
Shaft alignment as specified (see chapter Shaft alignment
and load).
Cooling circuit connected
and coolant flowing
Used coolant:
Power connections
Cable gland assembly as specified (cable gland to cables)
with correct cable diameter
Cable lug air cap (to metallic
≥10 mm
structures)
Cable lug tightening torque
13 Nm
(to the busbar)
Connection box cover bolts
4 Nm
tightening torque
Grounding
Electric machine enclosure grounding connected
Low voltage cable shield grounding connected
Power cable shield connection resistances to ground
(electric machine enclosure) measured and valid
68 |
©
Danfoss | July 2021
Electric machine installation checklist
Date:
N.A = Procedure not applicable PASS = Procedure passed FAIL = Procedure failed
N.A
☐
☐
☐
☐
☐
☐
☐
☐
☐
☐
☐
☐
☐
☐
Electric machine type (from the rating plate):
Electric machine serial number:
Date installed:
PASS
☐
☐
☐
☐
☐
☐
☐
☐
☐
☐
☐
☐
☐
☐
FAIL
☐
☐
☐
☐
☐
☐
☐
☐
☐
☐
☐
☐
☐
☐