Service Procedure Quick Reference
VAX Column Alignment
T200 - T380 - 680
Tools & Supplies
Estimated Time
ESD Protection
Library Power
Data I/O Operations
Robotic Movement
Admin./Superuser
BlueScale Login
Considerations
(continued next page)
Not a substitute for official published procedural guide
Detailed instructions/videos located at support.spectralogic.com
#2 Phillips screwdriver
7/64" Allen wrench
Lint-free/alcohol-free cloth
30 minutes
Required
Off
Discontinue
Verify with customer that data I/O to all drives has halted
Discontinue
Verify robotic movement has halted
Verify with customer that move requests from host have been halted
Required
It is recommended that all tapes are removed from drives by customer before
procedure to avoid potential stuck tapes after power-up
If library is installed in a rack, you must have full access to left side of library,
otherwise library must be removed from rack and placed on sturdy and level
work surface with access to power
o If removal of library from rack is not feasible, contact Spectra Technical Support
for alternate methods of performing this procedure
Use facility-approved safe method to move library into/out of rack. Work
surface must safely support weights noted below:
Max. Library Weight (Lbs./Kg)
Spectra recommends exporting all TeraPacks via TAP prior to removing library
from rack
T200
T380
428/194
627/285
1,211/549
T680
August 2017 V2
Page 1 of 4

Advertisement

Table of Contents
loading
Need help?

Need help?

Do you have a question about the T200 and is the answer not in the manual?

Questions and answers

Summary of Contents for Spectra T200

  • Page 1 If removal of library from rack is not feasible, contact Spectra Technical Support for alternate methods of performing this procedure ...
  • Page 2 Not a substitute for official published procedural guide Detailed instructions/videos located at support.spectralogic.com Service Procedure Quick Reference VAX Column Alignment T200 - T380 - 680  Considerations If library is removed from rack with TeraPacks remaining in library: (continued) o Before power up, verify all TeraPacks are correctly positioned in all chambers ...
  • Page 3 Not a substitute for official published procedural guide Detailed instructions/videos located at support.spectralogic.com Service Procedure Quick Reference VAX Column Alignment T200 - T380 - 680 Procedure Overview 7. If slot is NOT obstructed by either top or bottom section of HAX rod (continued) ...
  • Page 4 20. Power off library, replace service access panels (starting top to bottom) 21. Re-install library into rack (if removed) 22. Create an Auto-support Log File (ASL) and forward to Spectra Technical Support  Obtain permission from customer prior to performing this step ...