6.3 COMMON ALARMS—WHAT TO LOOK FOR
The CM 2000 and the CM 2000+ control modules have a wide range of alarming features that may be selectively enabled or disabled
to allow the monitoring and indication of trouble conditions. Described below are the different alarm conditions available on the
control module, their meanings, and possible causes.
Alarm
Description
High TS 1/ TS
This alarm will appear when the sensor
2 Temperature
temperature exceeds the HIGH TS TEMP ALARM
temperature setting.
Low TS 1/TS 2
This alarm will appear when the sensor
Temperature
temperature decreases below the LOW TS TEMP
ALARM temperature setting.
TS 1/ TS 2
This alarm will indicate if a temperature sensor is
Failure
not operating properly. The temperature sensor
may fail due to an "open" or "shorted" condition.
Control TS
This alarms a failure of the temperature sensing
Failure
element designated as the control element by the
TS CONTROL MODE setting. The output switch
may be latched off until this failure is corrected.
High Current
This alarms current levels that are greater than
the HIGH CURRENT ALARM setting for the
application.
Low Current
This alarms current levels that are less than the
LOW CURRENT ALARM setting.
High GFI
This alarms ground fault current levels which are
greater than the HIGH GFI ALARM setting.
GFI Trip
This value sets the upper limit of allowable ground
fault leakage. Exceeding this limit will result in
the output switch being latched off and the alarm
activated to indicate a ground fault condition.
50 | nVent.com
Cause of Alarm
• Alarm temperature setting too close to maintain temperature
• Flow of hot product
• Steaming out lines
• Incorrect TRACER wiring
• Alarm temperature setting too close to maintain temperature
• Flow of cold product
• Empty Pipe
• Damaged, wet, or missing insulation
• Heating cable not sized properly for the application or
damaged
• Incorrect or damaged field wiring - open leads or excessive
resistance, (either intermittent or continuous) may be due to
broken or damaged wires or loose terminals.
• Damaged or inoperative temperature sensors
• Incorrect or damaged field wiring - open leads or excessive
resistance (either intermittent or continuous) may be due to
broken or damaged wires or loose terminals.
• Damaged or inoperative temperature sensors
• The ATC signal from an ATC MASTER control module
is absent
• Alarm setting too close to normal operating current
• High in-rush current from "cold start" of self-regulating cable
• Damaged or partially shorted heating cable
• "As built" cable length is greater than design value
• Incorrect CURRENT TURNS RATIO setting
• Incorrect wiring
• Alarm setting too close to normal operating current
• Low source voltage
• Damaged or inoperative heating cable
• Open connection - wiring problem
• SSR or contactor failure (open)
• Incorrect CURRENT TURNS RATIO setting
• Alarm setting too close to normal leakage current
• Damaged cable insulation and/or moisture present
• Moisture in junction box
• Poor splice or termination
• Moisture provides conductive ground path which allows
ground fault current
• Trip setting too close to normal leakage current
• Damaged cable insulation and/or moisture present
• Moisture in junction box
• Poor splice or termination
• Moisture provides conductive ground path which allows
ground fault current