DOC. MIE12093 Rev. 1 Page 3 of 52 SHORT FOREWORD ............................... 4 INTRODUCTION................................5 1 TEST SET EXPLANATION ............................7 1.1 C ......................7 ONNECTION TO THE RELAY AND POWER 1.2 T ................................7 EST CONTROL 1.3 C ............................10 URRENT GENERATION 1.4 AC ......................
DOC. MIE12093 Rev. 1 Page 4 of 52 SHORT FOREWORD Dear T/1000 user, I often wondered why the user’s manual is not very much used, even if it includes valuable information. As me too I am a user of such manuals, the answer I have given myself is that valuable information are concealed somewhere in the thick thing, and I do not have time to waste to find it.
DOC. MIE12093 Rev. 1 Page 5 of 52 INTRODUCTION The single phase relay test set mod. T/1000 is suited for the testing and adjustments of the following types of relays; the table lists also the paragraph that explains the test procedure. Type of relay IEEE code PARAGRAPH...
Page 6
DOC. MIE12093 Rev. 1 Page 6 of 52 which operates with all WINDOWS versions, and allows creating a data base of all tests in the plant. The basic T/1000 function is to generate current and voltages and to stop generation as the relay trips.
DOC. MIE12093 Rev. 1 Page 7 of 52 1 TEST SET EXPLANATION 1.1 C ONNECTION TO THE RELAY AND POWER At first, be sure that the main control knob (6)is turned (rotated) to the zero position (complete counter-clockwise). The reason is that the current generator is actually a high current voltage generator.
Page 8
DOC. MIE12093 Rev. 1 Page 8 of 52 The following flow diagram summarises all available test control selections. Normal (default) Trip + pulse time Test mode Reclose mode Maintained Fault injection Momentary Timed TEST CONTROL External Test power OFF delay Save 1 period Don’t save...
Page 9
DOC. MIE12093 Rev. 1 Page 9 of 52 FAULT TRIP (STOP) RECLOSE (START) TIME MEASUREMENTS Other Fault injection selections: . Maintained (default): .. ON mode: fault outputs are generated until OFF is selected. .. ON+TIME or OFF+TIME: as the STOP input is sensed, T-1000 returns OFF. .
DOC. MIE12093 Rev. 1 Page 10 of 52 1.3 C URRENT GENERATION If the following current limits and time duration of main current outputs are trespassed, the generation is interrupted, and the operator is warned by an alarm message. 1) MAXIMUM POWER 300 VA RANGE CURRENT MAXIMUM...
DOC. MIE12093 Rev. 1 Page 11 of 52 . At first, be sure that the main control knob (6) is turned (rotated) to the zero position (complete counter-clockwise). . Power-on T-1000. . Select by the push-button (57) the measurement on the desired output sockets (13), according to the maximum current to be generated: the LED turns on;...
DOC. MIE12093 Rev. 1 Page 12 of 52 .. Power is not enough; the desired test current cannot be adjusted. If this occurs at high currents, the problem is that the burden is too high; the solution is either shortening wires or increasing their cross section (or both).
Page 13
DOC. MIE12093 Rev. 1 Page 13 of 52 not changed during all tests. It is possible to phase shift the current with respect to voltage; selections are the following. . Power-on T-1000: the AC voltage value is displayed. . There are three ranges available: 65; 130 or 260 V AC; the power is 30 W continuous; 40 W peak for 1 minute.
DOC. MIE12093 Rev. 1 Page 14 of 52 Once the nominal voltage is adjusted to the pre-fault value, it is possible to change the amplitude (V, SYN relays) or frequency (F, SYN relays), or angle (SYN relays: in this instance, the angle is referred to V main rather than to I main) or frequency rate of change (dF relays) of the fault voltage.
DOC. MIE12093 Rev. 1 Page 15 of 52 The second auxiliary generator can be used to supply the auxiliary DC voltage for the relay to be tested. To this purpose, the voltage is continuously available at sockets (63). Use this generator as follows.
DOC. MIE12093 Rev. 1 Page 16 of 52 The timer offers a number of possible selections to permit many different types of testing depending on the selection by the operator. The following flow shows all possible selections. Clean-voltage Internal N.O.-N.C.-Edge Start Count External...
DOC. MIE12093 Rev. 1 Page 17 of 52 (t>) tmax t>> I (I/IN) I> I>> . Set the “Automatic save at trip” function, as follows. Test control > Save > Confirm at trip > Save min > ESC NOTE: for other selections see the pop-up menu chapter. .
DOC. MIE12093 Rev. 1 Page 18 of 52 1.10.3. Second threshold trip and drop-off The second session is finding threshold I>>. The problem is that the test result criterion is no more to find the limit between no trip and trip; it is instead to find the limit between two different timings: what we have shown as t>, for currents less than I>>, and t>>...
Page 19
DOC. MIE12093 Rev. 1 Page 19 of 52 FAULT Stop Trip delay 5A) Overcurrent relay trip delay FAULT Stop Trip delay 5B) Undercurrent relay trip delay Let us consider for example the timing test of an over-something relay, where the trip contact is Normal Open.
DOC. MIE12093 Rev. 1 Page 20 of 52 . Now, press ON and pre-adjust the same set of fault parameters. . Select OFF+TIME: as the relay resets, pressing the multi-function knob drop-off values can be saved. Confirm save results pressing the multi-function knob, and proceed. With different test values, other timings can be measured.
DOC. MIE12093 Rev. 1 Page 21 of 52 t>> I> I>> I-t over-current relay curve The curve means that: . If the test current is less than I> no trip occurs; . For current more than I> and less than I>> trip time is a function of the test current; .
Page 22
DOC. MIE12093 Rev. 1 Page 22 of 52 I-V directional relay curve For instance, in order to find the point A it is apparent that the procedure is: . Set the voltage; . Increase the current until the relay trips. However, in order to find the point B the best procedure is: .
DOC. MIE12093 Rev. 1 Page 23 of 52 The area of intervention is the one within the circle with the centre in the negative X axis. The first problem is to convert R and X into the corresponding V, I, angle; then, the current is set at IN, and only voltage and phase are modified.
Page 24
DOC. MIE12093 Rev. 1 Page 24 of 52 . Connect the component terminals to the external voltage measurement: this avoids errors caused by the connection leads and by the current measurement circuit; . Select the desired measurement (Z+ f , or R+X); .
OFF+ MENU TIME TIME 300VA 60VA T1000 RELAY TEST SET RS232 250V The following list includes the key components inside T/1000; see the schematic on last page. 1) Main supply fuse, rated T10A, incorporated in the supply socket. 2) Power-on switch.
Page 26
DOC. MIE12093 Rev. 1 Page 26 of 52 15) Microprocessor board code YWA41300. 16) Converter board code YWA11401. 17) Front panel board; code YWA11398. 18) Auxiliary contact protection re-triggering fuse, rated 5 A. 19) Auxiliary DC voltage fuse, F2A. 20) Adjustment of auxiliary AC voltage output. 21) Adjustment of auxiliary DC voltage output.
DOC. MIE12093 Rev. 1 Page 27 of 52 2.2 D ISPLAY AND CONTROL LIGHTS At power-on, the following control lights turn on (default situation): . START: INT (31); NO VOLTAGE (35); . STOP: NORMAL OPEN (37) and NORMAL CLOSED (38) (EDGE selection); NO VOLTAGE (40);...
Page 28
DOC. MIE12093 Rev. 1 Page 28 of 52 The flux diagram of menu selections can be found in Appendix 1. LEVEL1 LEVEL 2 LEVEL 3 LEV. 4 FUNCTION TEST Test Normal (default) Measures the time delay from START (internal, CONTROL mode external) to STOP (internal, external).
Page 29
DOC. MIE12093 Rev. 1 Page 29 of 52 LEVEL LEVEL LEVEL LEVEL FUNCTION INT (default) Timer starts when ON or ON+TIME are activated TIMER Start START/ and outputs generated. STOP NO-NC- After ON or ON+TIME, timer starts on the external EDGE input.
Page 30
DOC. MIE12093 Rev. 1 Page 30 of 52 LEVEL LEV. LEV. LEVEL LEVEL 5 FUNCTION Range 65 (default) ; 130 ; 260 V. VAC/ Mode Fault (default) The auxiliary AC voltage is adjusted by the dedicated control knob, and is always present, independently by test start. If the auxiliary voltage should be applied along with the main current or voltage, go to next selection.
Page 31
DOC. MIE12093 Rev. 1 Page 31 of 52 LEVEL1 LEVEL LEVEL 3 LEVEL 4 FUNCTION Units of I Normal If selected, current values are displayed METERS Internal in A. I/IN If selected, displayed values are defined as I/IN, that can be defined. Units of V Normal If selected, voltage values are displayed...
Page 32
DOC. MIE12093 Rev. 1 Page 32 of 52 LEVEL1 LEVEL LEVEL 3 FUNCTION None (default) No extra measurement displayed METERS Other (continued) internal Active power P; W Reactive power Q; VAr Impedance module Z, Ohm Impedance argument f , ° Active impedance R, Ohm component...
Page 33
DOC. MIE12093 Rev. 1 Page 33 of 52 LEVEL1 LEVEL 2 LEVEL 3 LEVEL 4 FUNCTION Selected result(s) RESULTS Delete All results CONFIGU- Settings Save to address 1..10 Saves current settings to X RATION Restore address 1..10 Restores settings from X Restore default 1..10 Restores default settings UK, FR, SP, PT, GE, IT...
Murphy’s law, when it was most necessary. We at ISA do our best efforts to filter the so-called infant mortality of electronic components prior to delivery of all our test sets; and this after extensive testing of prototypes and pre-production units.
DOC. MIE12093 Rev. 1 Page 35 of 52 3.2 E RROR MESSAGES The test set performs a number of tests at power-on and during the generation. The following table lists all the messages, and the corrective action. A) TESTS AT POWER-ON (and runtime) ERROR MESSAGE CONSEQUENCE CORRECTIVE ACTION...
DOC. MIE12093 Rev. 1 Page 36 of 52 duration: wait until it cools down OVERTEMP T1000 Generation is stopped The test set temperature is too ENGINE high because of heavy loads or very long test duration: wait until it cools down 3.3 T...
DOC. MIE12093 Rev. 1 Page 37 of 52 3.4 P HYSICAL DESCRIPTION T/1000 components are accessed by removing the five screws that are located below it, and lifting the central part by the handles. There is a main board mounted on the front panel, and a number of components mounted on the back panel.
Page 38
DOC. MIE12093 Rev. 1 Page 38 of 52 The picture above shows the base with the auxiliary DC and AC modules removed. The following picture shows the front panel with the big control board. On the upper corner are mounted the control cards; their location is shown in the drawing below. Cards are kept in place by the piece of aluminium sheet on the right, and also by the threaded bar between the boards.
DOC. MIE12093 Rev. 1 Page 39 of 52 The two parts set apart are shown in the following picture. 3.4.1 Protection fuses By the side of the boards support is mounted a board with a set of protection fuses. They protect the following modules: .
DOC. MIE12093 Rev. 1 Page 40 of 52 On the edge of the CONV board are mounted a number of ring-shaped test points. They carry the key auxiliary supplies, which operate the test set. The arrangement of the test points is the following.
DOC. MIE12093 Rev. 1 Page 41 of 52 F 2 A F 3.15 A The last test is to remove the connector J800 coming from the big round power transformer. The connector has 4 pins: the voltage between pins 1 and 4 should be 155 V AC nominal; between pins 2 and 3 should be 11.5 V AC nominal.
If the backlight does not turn on, the converter is likely to be faulty. The converter replacement is performed as follows. . Remove T1000 from the container. . Go to the left side: the sketch below shows the main components.
DOC. MIE12093 Rev. 1 Page 43 of 52 3.9 T VOLTAGE MEASUREMENT IS NOT STABLE First of all, check that there is no unplugged connector or broken wire. Next, it is necessary to understand if the problem is in the measurement or if the output is actually unstable. To this purpose, connect the output to an AC voltage meter and verify the reading.
DOC. MIE12093 Rev. 1 Page 44 of 52 ON). - Insert again all the boards (and the INTE connectors too). - Turn on the test set. - At this point , the instrument should be connect to your PC. Execute the firmware download. Verify that the new firmware version appears;...
Page 45
DOC. MIE12093 Rev. 1 Page 45 of 52 INSTRUMENT RETURN FORM DATE ____________ AGENT _________________ COUNTRY ___________________ TYPE OF INSTRUMENT ____________________ SERIAL NO. __________________ INSTRUMENT RETURNED FOR: CALIBRATION ____ REPAIR ____ In case of repair, please specify the following. DATE OF FAULT _______________ REPORTED BY E-MAIL, PHONE ___________ COMPANY _____________________ USER’S REFERENCE ____________________ FAULT DESCRIPTION ____________________________________________________ _______________________________________________________________________...
DOC. MIE12093 Rev. 1 Page 46 of 52 3.14 C ALIBRATION 3.14.1 Introduction T/1000 does not need to be calibrated, as metering circuits employ high stability components. It is suggested to check the unit every 3 years, by comparing T/1000 measurements to external meters.
DOC. MIE12093 Rev. 1 Page 47 of 52 3.14.3 T/1000 output calibration The internal measurements calibration is performed by generating the following current and voltage outputs. For each output range there is a number of measurement scales, that are separately adjusted: during the use T/1000 automatically selects the best scale.
Page 48
DOC. MIE12093 Rev. 1 Page 48 of 52 OUTPUT RANGE SCALE CALIBRATION LINEARITY NOTE FOR OFF-SET VALUE TEST CALIBRATION Auxiliary 65, 130 1,999 V Voltage sockets shorted V AC 19.99 V 10 V 20 V Voltage sockets shorted voltage 59.99 V 50 V 60 V Voltage sockets shorted...
DOC. MIE12093 Rev. 1 Page 49 of 52 3.14.4 T/1000 external measurements calibration The external measurements calibration is performed using T/1000 as the source. As for the measurement of internal parameters, for each input range there is a number of measurement scales, that are separately adjusted: during the use T/1000 automatically selects the best scale.
DOC. MIE12093 Rev. 1 Page 50 of 52 APPENDIX 1 SPARE PARTS LIST The following is the suggested list of spare parts for a duration of five years and for up to five test sets. The reference is made to the list of components. 1) N.
Page 52
Normal (default) Trip + pulse time Test mode DOC. MIE12093 Rev. 1 Page 52 of 52 Reclose mode Maintained (default) Fault injection Momentary External TEST CONTROL Timed Output power OFF delay Save Don’t save (default) Automatic at trip Confirm at trip Auxiliary contact Manual...