netsc_ipnetmask – Netmask for the system controller subnet
Note – For more information on configuring ALOM CMT, refer to the Advanced
Lights Out Management (ALOM) CMT Guide.
To configure these parameters you must use the setsc command. The usage is:
sc> setsc parameter
1. Set the netmask for the system controller.
sc> setsc netsc_ipnetmask 255.255.255.0
This example uses 255.255.255.0 to set the netmask. Your network environment
subnet might require a different netmask. Use a netmask number most appropriate
to your environment.
2. Set the IP address for the system controller.
sc> setsc netsc_ipaddr service-processor-IPaddr
3. Set the IP address for the system controller gateway.
sc> setsc netsc_ipgateway gateway-IPaddr
4. Set the if_network parameter to true.
sc> setsc if_network true
5. Use the showsc command to verify that the parameters were set correctly.
The showsc command displays all the configuration parameters and their values, as
shown in the example below.
50
SPARC Enterprise T1000 Server Installation Guide • April 2007