During machine operation the temperature in the room increases. This results in need for ventilation. A ventilation kit
can be ordered; 988 80 20 43.
The thermostatically controlled fan (A) is mounted on the wall behind the machine. The thermostat is mounted further
into the room.
The fresh air intake (B) must end in the room in front of the machine positioned diagonally from the fan.
The need for fresh air varies and is controlled by the thermostat.

6.2 Fresh air

For maximum efficiency and the shortest possible drying time, it is important to ensure that fresh air is able to enter
the room from the outside in the same volume as that blown out of the room
To avoid draught in the room it is important to place the air inlet behind the machine.
The area of the air inlet opening is recommended to be five times the size of the exhaust pipe area. The area of the
inlet opening is the area through which the air can flow without resistance from the grating/slatted cover.
The resistance in the grating/slats on the air inlet cover panel should not exceed 10 Pa (0.1 mbar).
Note!
Gratings/slatted covers often block half of the total fresh air vent area. Remember to take this into account.