Main Menu Buttons -
Installation Settings
Heat & Cool Stages
Heat & Cool Stages
Up to 2 Stages Cooling and 4 stages Heating.
Compressor Stages
Up to 2 compressors.
Aux Heat Stages
0 to 2 stages of Aux Heating.
Timers & Deadbands
Cycles Per Hour
At 6 cycles per hour, the HVAC unit will only be allowed to
energize once every 10 minutes. The Cycles Per Hour limit
may be overridden and reset by pressing the WARMER or
COOLER buttons. (2, 3, 4, 5, 6, No Limit)
Min Heat/Cool Difference
The minimum gap between Heat and Cool setpoints. (0 - 6 deg. F)
Compressor Min OFF Time
None, 3 minutes, or 5 minutes.
Settings
(1h1c)
(1h1c)
}
(1h1c)
(1h1c)
(6)
(2˚)
(5m)
54
Only available when
dip switch is set for
Heat Pump operation.