Default Function - Johnson Controls T7600 Installation Manual

Lcd digital thermostat
Hide thumbs Also See for T7600:

Advertisement

T7600
PARAMETER SETTING (PART 2/2)
T7600-
T7601-
T7600-
TF21-
TF20-
TF20-
Code
...JS0
...JS0
...JS0
11
---
---
12
---
---
13
14
15
16
17
18
19
20
21
22
23
25
26
27
28
---
29
30
---
31
---
32
---
33
---
34
---
37
P/N 24-85784-00151 Rev. F Issue Date: 10 2020
T7603-
T7600-
T000-
TB21-
...JF0
...JA0
Parameter Name
---
---
ECM Max voltage
---
---
ECM cut off relay (F-ON)
Restart after power failure
Keypad lock
Default display
---
Auto changeover
Digital input function
(OCC)
Unit selection
Temperature offset
Fan speed (ECM not
---
applicable when auto
mode)
Language
---
Mode selection
Back light
Remote sensor type
MODBUS address
Baud rate
---
Sample time
Deadband
KP (proportional control
---
gain, PB = 100/KP)
---
KI (integral control gain)
TiO2/ESP operation
---
---
Inter stage difference
---
---
Heating stage
---
---
Fan off timer (time
postpone setting for
---
fan off)

Default Function

Max voltage above which the fan output is 100%,
10V
range 0 V-10 V. The adjustment is 0.5V for every step
00: Disabled
00
01: Enabled
00: Keep last status
00
01: On
02: Off
00: No lock
01: Lock all keys
02: Lock the keys except Fan Speed and Temp Adjustment keys
00
03: Lock the ON/OFF and Timer keys
04: Lock the keys except ON/OFF key
00: Display room temp.
00
01: Display setpoint only
00: Disable
00
01: Enable (when 2 pipe requires 10K NTC on water tube)
00: Setpoint reduction when contact is Closed (UnOccupied)
01: Setpoint reduction when contact is Open (UnOccupied)
02: Dew Point Alarm when contact is Closed
00
03: Dew Point Alarm when contact is Open
04: Shut off Fan and Valves when contact is Closed
05: Filter Alarm when contact is Closed
06: Filter Alarm when contact is Open
00: Celsius degree (°C)
00
01: Fahrenheit degree (°F)
0
Setting range -5°C to 5°C (-9°F to 9°F)
00: 3 Speed
01: 2 Speed (Wiring MED, LOW)
00
02: 1 Speed (Wiring LOW)
03: No Fan
00: Chinese
00
01: English
00: Cooling/heating/ventilation
01: Cooling only
00
02: Heating only
30
The back light will be OFF in 05 seconds to 60 seconds.
00: China market 10k NTC
00
01: JCI type II 10k NTC
1
1-64
00: 9600
00
01: 4800
10
Setting range 1 second to 99 seconds
1
Setting range 0°C to 10°C (32°F to 50°F)
10
Setting range 1 to 99
01
Setting range 0 to 99
00: Operate separately (Press the General button for a short
00
period)
01: Work in parallel with FCU fan
3
Setting range 0°C to 10°C (32°F to 50°F)
00: 2 Stages
00
01: 1 Stages
00
00 seconds- 99 seconds
English