Configuration Option
Occupied Cool Setpt Stop
Not Occupied Heat Setpoint
Standby Heat Setpoint
Occupied Heat Setpoint
Occupied Cool Setpoint
Standby Cool Setpoint
Not Occupied Cool Setpoint
Event 1 State
Event 2 State
Event 3 State
Event 4 State
Event 1 Time
Event 2 Time
Event 3 Time
Event 4 Time
a
The Factory defaults listed here apply to all subbase models with the exceptions of the items listed in Table 18.
b
12:00 Noon is the default start point when time is unknown.
c
Only Available if user selected one or more of following: Dehumidification Reset, Dehumidification Minimum On, or Dehumidification Reheat.
d
Keypad/LCD cannot handle Standby setpoints. Keypad users cannot set Occupied setpoints that violate Not Occupied setpoint relationship. The T7350
algorithm never allows the effective setpoint outside Not Occupied setpoints.
Table 18. Exceptions to Factory Defaults.
Configuration Option T7350A T7350B T7350D T7350M
Heat Output Stages
1
Cool Output Stages
1
Room Humidity Sensor None
Heat Throttling Range 3
Cool Throttling Range
3
Heat Integral Time
3100
Cool Integral Time
3100
Table 17. Thermostat Setup Options Through PDA. (Continued)
PDA
Keypad
a
Factory Default
Tool
/ LCD
85°F
X
55°F
X
X
67°F
X
d
70°F
X
X
75°F
X
X
78°F
X
d
85°F
X
X
Occupied
X
X
Not Occupied
X
X
None
X
X
None
X
X
8:00 a.m.
X
X
10:00 p.m.
X
X
12:00 a.m
X
X
(midnight)
X
X
2
3
0
2
3
0
None
Local
Local
4
7
5
4
7
5
2500
1650
1250
2500
1650
1250
T7350 COMMERCIAL PROGRAMMABLE THERMOSTAT
Occupied Maximum Cool Setpoint: Highest the programmed occupied cooling setpoint
can be adjusted. Range: 45 to 99°F. Value ≥ OccCl ≥ OccHt + 2°F.
Not Occupied heating setpoint. Range: 40 to 90°F.
UnoccHt ≤ OccHt ≤ OccCl - 2°F; UnoccHt ≤ StdByHt ≤ StdByCl - 2°F
Standby heating setpoint. Range: 40 to 90°F.
Occupied heating setpoint. Range: 40 to 90°F.
Occupied cooling setpoint. Range: 45 to 99°F.
Standby cooling setpoint. Range: 45 to 99°F.
Not Occupied cooling setpoint. Range: 45 to 99°F.
UnoccCl ≥ OccCl ≥ OccHt + 2°F; UnoccCl ≥ StdByCl ≥ StdByHt + 2°F.
Day Schedule is a structure of 8 days of 4 events each day. Defaults listed are for
Monday through Friday. Saturday/Sunday/Holiday default to Unprogrammed (None /
12:00 a.m.). All Events can be set for: Standby or None.
Only Events 1 and 3 can be set for Occupied.
Only Events 2 and 4 can be set for Not Occupied.
Note: The keypad/LCD can't set an event to Standby, but it can change the time.
Scheduled time for event change.
12:00 p.m.: Noon
12:00 a.m.: Midnight
31
Description
63-2605—2