T7350 COMMERCIAL PROGRAMMABLE THERMOSTAT
Configuration Option
Key Pad (Lockout)
Recovery Heat RampMin
Recovery Heat RampMax
Recovery Cool RampMin
Recovery Cool RampMax
Recovery Heat OAT@Min
Recovery Heat OAT@Max
Recovery Cool OAT@Min
Recovery Cool OAT@Max
Demand Limit Control Bump
Power Failure Seq Start
Enable DAT High Limit
Enable DAT Low Limit
High Limit DAT Setpoint
Low Limit DAT Setpoint
Dehumidification Min On
Dehumidification Min On Time 5
Dehumidification Reset Temp None
Dehumidification Reset Temp
Setpt
Dehumidification Reheat
Dehumidification High Limit
Clock Year
Clock Month
Clock Day
Clock Minutes
Holiday Month
Holiday Day
Holiday Duration
Delays
System Switch
Fan Switch
Occupied Heat Setpt Stop
a
The Factory defaults listed here apply to all subbase models with the exceptions of the items listed in Table 18.
b
12:00 Noon is the default start point when time is unknown.
c
Only Available if user selected one or more of following: Dehumidification Reset, Dehumidification Minimum On, or Dehumidification Reheat.
d
Keypad/LCD cannot handle Standby setpoints. Keypad users cannot set Occupied setpoints that violate Not Occupied setpoint relationship. The T7350
algorithm never allows the effective setpoint outside Not Occupied setpoints.
63-2605—2
Table 17. Thermostat Setup Options Through PDA. (Continued)
PDA
Keypad
a
Factory Default
Tool
/ LCD
Enable All
X
X
5°F/hr
X
8°F/hr
X
3°F/hr
X
6°F/hr
X
0°F
X
40°F
X
90°F
X
70°F
X
3 °F
X
0 (x10 sec)
X
None
X
None
X
110°F
X
45°F
X
None
X
X
X
2 °F
X
None
X
65%
X
c
X
1999
X
12
X
Wed
X
X
X
b
11:15 p.m.
0
X
0
X
0 days
X
On
X
X
Auto
X
X
On
X
X
55°F
X
Keypad lockout enable/disable through special keypad sequence.
Enable All (0): No lockout.
SetPts & Ovrrd (1): Lockout all keys except: Temporary (Not) Occupied,
.
Info Only (2): Lockout all keys except
The special keypress features are never locked out.
Minimum heating recovery ramp rate. Range: 0 to 20°F/hr.
Maximum heating recovery ramp rate. Range: 0 to 20°F/hr.
Minimum cooling recovery ramp rate. Range: 0 to 20°F/hr.
Maximum heating recovery ramp rate. Range: 0 to 20°F/hr.
Minimum heating outdoor air temperature. Range: -20 to 100°F.
Maximum heating outdoor air temperature. Range: -20 to 100°F.
Minimum cooling outdoor air temperature. Range: -20 to 100°F.
Maximum cooling outdoor air temperature. Range: -20 to 100°F.
Demand limit control set point bump. Range: 0 to 10°F.
Delays start of equipment (fan, heat, cool) after power restored to thermostat.
Range: 0 to 150 seconds (in 10-second increments).
None: No Discharge Air Temperature (DAT) high limit; Enable: Use DAT High Limit.
None: No Discharge Air Temperature (DAT) low limit; Enable: Use DAT Low Limit.
Discharge Air Temperature High Limit Setpoint. Range: 65 to 140°F.
Discharge Air Temperature Low Limit Setpoint. Range: 35 to 60°F.
None: No Minimum On Time dehumidification;
Enable: Dehumidification using Minimum On Time.
Minimum on time used with "Dehumidify Minimum On". Range: 5 to 15 minutes.
None: No Reset dehumidification; Enable: Dehumidification using Reset.
Amount of reset used with "Dehumidify Reset". Range: 1 to 5 °F.
Must be smaller than occupied zero energy band (ZEB) or standby ZEB.
None: No Reheat dehumidification; Enable: Dehumidification using Reheat.
Dehumidification High Limit. Range: 10 to 90%.
Range: 2000 to 2035.
1: January... 12: December.
Day of the Week: Sun, Mon, Tue, Wed, Thu, Fri, Sat
12:00 a.m.: Midnight (first minute of the day); 12:00 p.m.: Noon.
Unprogrammed; January...December.
Unprogrammed; 1; 2...31; LASTDAYOFMONTH...LAST_SAT
Duration of given Holiday (in days). Range: 0 to 99 days.
On: Delays (on relays, sequential start, etc.) are active.
Off: Delays disabled (also called Test Mode).
System settings: Auto; Cool; Off; Heat; Emergency Heat (valid if Heat Pump)
Fan setting: On; Auto
Occupied Minimum Heat Setpoint: Lowest the programmed occupied heating setpoint
can be adjusted. Range: 40 to 90°F; Value ≤ OccHt ≤ OccCl - 2°F.