Troubleshooting Guide (Table 16) - Honeywell T7350 User Manual

Commercial programmable thermostat
Hide thumbs Also See for T7350:
Table of Contents

Advertisement

TROUBLESHOOTING GUIDE (TABLE 16)

Symptom
Display will not come on. Thermostat is not being powered.
Temperature display is
incorrect.
Temperature settings will
not change.
(Example: Cannot set
heating higher or cooling
lower.)
Room temperature is out
of control.
Heat will not come on.
Table 16. Troubleshooting Information.
Possible Cause
Room temperature display has been
recalibrated.
Thermostat is configured for °F or °C
display.
Bad thermostat location.
Display shows three dashes and a degree
sign (all systems shut down).
Upper or lower temperature limits were
reached.
Occupied setpoint temperature range
stops were configured.
Keypad is locked. When a locked key is
pressed, LOCKED appears momentarily
on the LCD.
Remote temperature sensing is not
working.
No power to the thermostat.
Thermostat minimum off time is activated. • Wait up to five minutes for the system to respond.
System selection is set to Off or Cool.
DAT high limit has been reached, or
OAT lockout is engaged.
T7350 COMMERCIAL PROGRAMMABLE THERMOSTAT
Check that X terminal is connected to the system
transformer.
Check for 24 Vac between X and RH or RC terminals.
If missing 24 Vac:
• Check if circuit breaker is tripped; if so, reset circuit
breaker.
• Check if system fuse is blown; if so, replace fuse.
• Check if the HVAC equipment power switch is in the
Off position; if so, set to the On position.
• Check wiring between thermostat and HVAC
equipment. Replace broken wires and tighten loose
connections.
If 24 Vac is present, proceed with troubleshooting.
Use PDA configuration software to recalibrate as desired.
Press both Run Schedule and Copy, then reconfigure the
display.
Relocate the thermostat.
T7350 is set for remote sensing and sensor is missing or
circuit is either open or shorted.
Check the temperature setpoints:
• Heating limits are 40 to 90°F (7 to 31°C)
• Cooling limits are 45 to 99°F (9 to 37°C)
Using a PDA, check setpoint stops. If necessary,
reconfigure the stop(s).
• Use PDA (Set, Display) to unlock keypad.
• Press both Run Schedule and Copy, then change
keypad lock level.
Check all remote sensors.
Check that X terminal is connected to the system
transformer.
Check for 24 Vac between X and RH terminals.
If missing 24 Vac:
• Check if circuit breaker is tripped; if so, reset circuit
breaker.
• Check if system fuse is blown; if so, replace fuse.
• Check if the HVAC equipment power switch is in the
Off position; if so, set to the On position.
• Check wiring between thermostat and HVAC
equipment. Replace broken wires and tighten loose
connections.
If 24 Vac is present, proceed with troubleshooting.
• Use PDA to configure heating response.
Set system selection to Heat or Auto.
• If the setpoints are correct, do nothing.
• Use PDA (Heating Config) to adjust or disable DAT
high limit and/or OAT lockout.
• Check HVAC equipment to ensure proper operation.
19
Action
63-2605—2

Hide quick links:

Advertisement

Table of Contents
loading

Table of Contents