Honeywell T7350 System Engineering page 6

Commercial programmable thermostat
Hide thumbs Also See for T7350:
Table of Contents

Advertisement

T7350 COMMERCIAL PROGRAMMABLE THERMOSTAT
Mounting Means:
Mounts on subbase.
Subbase Mounts On:
Wall: Using two 5/8 in. long #6-32 screws (included).
Outlet Box: Using sheet metal screws.
Throttling Range for Modulating Outputs:
Automatically adjusts based on heat/cool stages. Manually
adjustable with PDA.
Clock Accuracy (at 77°F [25°C]): ±1 min./month (30 days).
Minimum Stage Operation Time (fixed):
Minimum On
Heat: 1 minutes.
Cool: 3 minutes.
Minimum Off (Cool and Heat Pump): 1 minute.
Electrical Ratings:
Power: 24 Vac, 50/60 Hz.; 20 to 30 Vac, 50/60 Hz.
Input:
Temperature: 20K ohms.
Humidity: 0-10 Vdc.
Outdoor: 3000 PTC.
Discharge Air: 20K ohms.
Occupancy Sensor: Dry contact switching 30 Vdc at 1 mA.
All Relay Outputs (at 30 Vac):
Running: 1.5A maximum.
Inrush: 7.5A maximum.
Modulating Output: 4 to 20 mA with 510 ohm maximum
terminating resistance.
System Current Draw (without load):
5 VA maximum at 30 Vac, 50/60 Hz.
NOTE: Relays are N.O. Single-Pole, Single-Throw (SPST).
Outdoor Sensor Wiring: Requires 18 gauge wire.
Humidity Ratings: 5% to 90% RH, noncondensing.
Emergency Heat Indication:
Display indicates when Emergency Heat is activated (Em).
Temperature:
Ratings:
Operating Ambient: 30°F to 110°F (-1°C to 43°C).
Shipping: -30°F to +150°F (-34°C to +66°C).
Display Accuracy: ±1°F (±1°C).
Setpoint:
Range:
Heating: 40°F to 90°F (4°C to 32°C).
Cooling: 45°F to 99°F (7°C to 37°C).
Deadband: 2°F (1°C).
Default Settings: See Table 5.
Loss of Power: The thermostat maintains programmed times
and temperatures for the life of the product. Clock and day
information is retained for a minimum of 48 hours.
NOTE: To achieve the 48-hour power-loss clock retention,
the T7350 must be powered for at least 5 minutes.
63-4368
Communicating Model T7350H:
Connection Terminals for the L
Network jack for quick access by personal computer based
tools.
Communications service-pin pushbutton to simplify startup.
®
L
M
Functional Profile: 8500_20 Space Comfort
ON
ARK
Controller.
®
L
M
SCC Object Type: 8504 Rooftop See Fig. 3.
ON
ARK
ARK ®
L
M
Program Identifier: 80:00:0C:55:04:03:04:2E.
ON
®
L
M
Application Interoperability: version 3.3
ON
ARK
Honeywell L
M
ON
ARK
http://plugin.ge51.honeywell.de/index.htm#
PDA System Requirements:
Palm OS: 3.5.x to 5.2.1
Dynamic Heap: 256K bytes.
Free RAM Space: 1000K bytes.
Serial Communications: RS232.
Approvals:
European Community Mark (CE) Listed.
UL 873 Recognized, NEC Class 2.
FCC Part 15 subpart J Class A.
cUL.
Table 5. Default Setpoints.
Control
Occupied
Heating
70°F (21°C)
Cooling
75°F (24°C)
Accessories:
Duct Discharge Air Sensors: C7041B (6 or 12 in.),
C7041C (18 in.), C7041J (12 ft averaging),
C7770A (8 in. probe).
Outdoor Air Sensors: C7089A, C7170A,
C7031G2014 (weatherproof).
Temperature Sensors (Remote): C7772A, T7770A1006,
T7770B1046, T7770C1044, T7770D1000, T7771.
Economizer Logic Modules: W6210, W6215, W7210, W7212,
W7215, W7459.
Humidity Sensors: H7625A,B; H7635A,B,C, H7655B.
PDA Units: Palm™ V, M125, and i705 handhelds;
TRGPro™ handheld; ZIRE™ 71 handheld;
TUNGSTEN™ T handheld.
Others:
209541B FTT network termination module.
209651A Vertical Mounting Hardware Wallplate Adapter
(Trident white).
50000083-001 Thermostat Interface Module (TIM).
50000452-001 Troubleshooting Cable.
AK3797 Single pair network cable plenum rated,
U.L. Type CMP.
AK3798 Single pair network cable, U.L. Type CMR.
AK3799 Double pair network cable plenum rated,
U.L. Type CMP.
Q7740A FTT network 2-way repeater.
Q7740B FTT network 4-way repeater.
TG511, TG512 Universal Versaguard™ Thermostat
guards.
6
®
W
Bus.
ON
ORKS
®
Plug-In file downloads:
Not
Occupied
55°F (13°C)
85°F (29°C)
Standby
67°F (19°C)
78°F (26°C)

Hide quick links:

Advertisement

Table of Contents
loading

Table of Contents