T7350 COMMERCIAL PROGRAMMABLE THERMOSTAT
Nv Name
L
ON
nviOccSensor
Occupancy Sensor In
nviOutdoorTemp
Outdoor Temperature In
nviPgm
Program In
nviRequest
Request
nviSetpoint
Setpoint In
nviSpaceRH
Space Humidity In
nviSpaceTemp
Space Temperature In
nviTimeSet
Time In
63-4368
Table 21. T7350H Network Variable Summary. (Continued)
S
™ Ref Name
Class
PEC
IN
IN
IN
IN
IN
IN
IN
IN
There are 3 distinct modes of operation: local occupancy sensor,
network occupancy sensor, or none.
The network occupancy input is nviOccSensor. It is bound from
another sensor or controller with occupancy status.
Occupancy sensor input from a network device:
0: OC_OCCUPIED
1: OC_UNOCCUPIED
-1: OC_NUL not connected (mains power up and fail detect
value).
Others: same as OC_NUL.
NOTE: If nviOccSensor is not invalid (OC_NUL), nviOccSensor
is used as the occupancy sensor even if another sensor
or no sensor is configured.
Outdoor temperature input from a network device. Ignored unless
nciConfig.oDAirSensor specifies a network configuration.
327.67: means to ignore comODTemp.
327.67: mains power up and failure detect value.
NOTE: If nviOutdoorTemp is not invalid (327.67), nviOutdoor-
Temp is used as the outdoor temperature even if another
sensor or no sensor is configured.
Memory address and data being sent to cover assembly flash
memory.
Input variable for managing network requests for status.
Desired space temperature (Celsius) set by remote network
device.
327.67: means to ignore nviSetPoint.
327.67: mains power up value.
Space humidity input (percent) from a network device. Ignored
unless nciConfig.humiditySensor specifies a network
configuration.
163.83: mains power up and failure detect value.
NOTE: If nviSpaceRH is not invalid (163.83), nviSpaceRH is
used as the space relative humidity even if another sen-
sor or no sensor is configured.
When configured for a network sensor and periodically updated,
the network space temperature sensor will override both the local
and remote sensors.
Space temperature input (Celsius) from a network device. Values
less than -2.2 will be clipped to -2.2. Values greater than 60 will be
clipped to 60.
327.67: means to ignore nviSpaceTemp.
327.67: mains power up and failure detect value.
NOTE: If nviSpaceTemp is not invalid (327.67), nviSpaceTemp is
used as the space temperature even if another sensor or
no sensor is configured.
Set current month, day, year, hour, minute, second
Time synchronization will be to a network device that has been
designated as the "time master." Time synchronization will occur at
the Guaranteed Periodic Update rate (typically every 55 seconds).