Preface Thank you for your support. Please read this manual carefully before use.The correct use will maximize the performance and advantages of the product, and bring you a good experience. When receiving the instrument, please open the package carefully, check whether the instrument and accessories are damaged by transportation and whether the accessories are complete.
Instrument installation 10 mm 98 mm 120 mm MENU Instrument dimensions Instrument dimensions(Side view) Embedded installation Installation of back cover with waterproofing seal 93 mm (± 0.5 mm) Embedded mounting Cut-out size Embedded the instrument into the square hole, and fix it with the provided clasp.
Wall mounted installation a.Install the mounting bracket on the wall first (M4 screw). b.Along the slot,clamp the instrument on the mounting bracket 53 mm Wall mounted Dimension of Mounting Bracket installation diagram Fixed bracket (M4 screw) is Insert the instrument into the installed on the wall first.
Instrument connection NO 1 COM 1 Temp NC 1 Temp NO 2 COM 2 NC 2 Pow DC+ Pow ACL (9~36V) (85~265V) Cur 1+ Pow DC- Pow AC N Com - Pow PE Pow PE Cur 2+ RS485 B RS485 A Electrical connection Connection between instrument and sensor: Connection of power supply, output signal, relay contacts and instrument baseplate.
Keypad descriptions Keypad operation tips: Short Press: Short Press means to release the key immediately after pressing. ((Default to short presses if not indicated below) Long Press: Long Press is to press the button for 3 seconds and then release it. Press and hold: Press and hold means to press the button, and accelerate after a certain time until the data is adjusted to the user's required value before releasing the button.
Display descriptions All pipe connections and electrical connections should be checked before use. After the power is switched on, the meter will display as follows. Main measurment+ Unit Instrument type Free Chlorine 8.025 mg/L 7.01pH 25.0 Temp. + Unit °C Automatic 14.51 mA temp.
Menu structure The following is the menu structure of this instrument,press MENU key to enter menu setting mode: If the monitor prompts you to enter the calibration security password, press the【▼】 key or 【 】key to set the calibration security password, and then press the 【ENT】key to confirm the calibration security password.No initial password here,please enter directly by press【ENT】key.
Page 12
Main Output Current 1 Channel Temperature 4-20mA Output Option 0-20mA 20-4mA Upper Limit Lower Limit Main Current 2 Channel Temperature 4-20mA Output Option 0-20mA 20-4mA Upper Limit Lower Limit 4800BPS RS485 Baud Rate 9600BPS 19200BPS None Parity Check Even 1 Bit Stop Bit 2 Bit 001+...
Calibration Press [MENU] to enter the setting mode and select the calibration Calibration Standard Calibration Point 1 0.01 (Default, can be modified) Solution Calibration Point 2 2 (Default, can be modified) Calibration Calibration Point 3 5 (Default, can be modified) Calibration Point 4 10 (Default, can be modified) Calibration Point 5...
Page 14
Field Calibration Select on-site calibration methods: Linear calibration , Offset adjustment , linear adjustment . Field Calibration When the data from laboratory or portable instrument are input into this item, the instrument will automatically correct the data. Free Chlorine Free Chlorine Field Calibration Field Calibration pH / ORP...
MODBUS RTU General Information The hardware version number of this document is V2.0; the software version number is V5.9 and above. This document describes the MODBUS RTU interface in details and the target object is a software programmer. MODBUS command structure Data format description in this document;...
Page 16
MODBUS RTU Transmission Mode When the instrument uses RTU (Remote Terminal Unit) mode for MODBUS serial communication, each 8-bit byte of information contains two 4-bit hexadecimal characters. The main advantages of this mode are greater character density and better data throughput than the ASCII mode with the same baud rate.
Page 17
Implementation of MODBUS RTU in Instrument According to the official MODBUS definition, the command starts with a 3.5 character interval triggering command, and the end of the command is also represented by a 3.5 character interval. The device address and MODBUS function code have 8 bits. The data string contains n*8 bits, and the data string contains the starting address of the register and the number of read/write registers.
Page 18
MODBUS function code 0x10: write multiple registers This function code is used to write continuous registers to remote devices (1... 123 registers) block that specifies the value of the registers written in the request data frame. Data is packaged in two bytes per register.
Page 19
Data format in instrument Overview Floating Point Definition: Floating point, conforming to IEEE 754 (single precision) Description Symbol Index Mantissa 30…23 22…0 22…0 Index Deviation Figure 14: floating point single-precision definition (4 bytes, 2 MODBUS registers) Example: Compile decimal 17.625 to binary Step 1: Converting 17.625 in decimal form to a floating-point number in binary form, first finding the binary representation of the integer part 17decimal= 16 + 1 = 1×2...
Page 20
If it is large-end storage mode, after executing the above statement, the data stored in outdata of address unit is 0x41 Outdata + 1 stores data as 0x8D address unit (outdata + 2) stores data as 0x00 address unit (outdata + 3) stores data as 0x00 2.
Page 21
Read instruction mode The communication protocol adopts MODBUS (RTU) protocol. The content and address of the communication can be changed according to the needs of customers. The default configuration is network address 01, baud rate 9600, even check, one stop bit, users can set their own changes;...
Complete Set Quantity Product Description 1) T4055 Online Residual Chlorine Meter 2) Instrument Installation Accessories 3) Operating Manual 4) Qualification Certificate Note: Please check the complete set of instruments before use. The company's other series of analytical instruments, please login to our website for enquiries.
1.LCD display is not bright Possible causes:Instrument or LCD Screen power supply failure. Solutions:Check whether the power supply is connected or not, and check whether the power supply wire of the sensor is connected in the wrong direction. 2.No current output Possible causes:It could be a fault in the current module or a wiring fault.
Warranty We Instruments warrants this product to be free from significant deviations in material and workmanship for a period of one year from the date of purchase. If repair is necessary and has not been the result of abuse or misuse within the warranty period, please return to We Instruments and amendment will be made without any charge.
Notes Distinguished users, please pay attention to the following points when using the instrument, in order to ensure the life and accuracy of the instrument. Careful handling to avoid collision and falling instruments in use. Avoid contact with water or other liquids during use. Don't put the instrument in the sunshine for a long time.
Page 28
Shanghai Chunye Instrument Technology Co.,Ltd Tel: 021-61621082 Fax: 021-61621099 Web: www.twinno.net Add: Building 6, No.166 Mindong Road, Pudong New District, Shanghai, China Post code:201209...