E0016
Fault of output phase
E0017
Inverter overload
E0018
Inverter output is
unloaded
E0019
Motor Overload
E0020
Reserved
E0021
Access fault of Control
Board EEPROM
ï
Output phase disconnection or loss
Heavy imbalance of inverter's three-
ï
phase load
ï
Acceleration time is too short
ï
Improper setting of V/f curve or
torque boost leads to over
current
ï
Instant power-off occurs, the running
motor is restarted
ï
Mains supply voltage is too low
ï
Motor load is too high
ï
Load disappeared or comes
down suddenly
ï
Parameters are not set properly
ï
Improper setting of V/f curve
ï
Mains supply voltage is too low
ï
Normal motor runs for a long time
with heavy load at low speed
ï
Motor runs with blocked torque
or load is too heavy
ï
Memory circuit fault of control board
EEPROM
ï
Please check the
connection
between inverter
and motor
ï
Please check the quality
of motor
ï
Adjust acceleration time
(F03..01,F03.03, F03.05,
F03.07)
Adjust V/f curve (F09.00 –
ï
F09.06) or torque boost
(F09.07,F09.08)
ï
Please set start mode to
be speed tracking
(F02.00=2)
ï
Please check mains
supply voltage
ï
Please use inverter with
proper power rating
ï
Please check load and
mechanical transmission
devices
ï
Please set the parameters
properly (F20.03-F20.05)
ï
Adjust the setting of V/f
curve (F09.00-F09.06)
ï
Check the power input
ï
Please use special
motor if the motor needs
to operate for a long time
with heavy load
ï
Please check the load and
mechanical transmission
devices
ï
Please contact the
supplier for repairing