E0008
Fault of power module
E0009
Heatsink overheat
E0010
Fault of braking unit
E0011
CPU fault
E0012
Parameters auto-tuning
fault
E0013
Contactor is not
actuated
E0014
Fault of current
detection
circuit
E0015
Fault of input phase
ï
Short circuit between phases output
ï
Short circuit to the ground
ï
Output current is too high
ï
Power module is damaged
ï
Ambient temperature is too high
ï
Inverter external ventilation is
not good
ï
Fan fault
ï
Fault occurs to temperature
detection circuit
ï
Circuit fault of braking unit
ï
CPU abnormal
ï
Parameter auto-tuning is time out
ï
Contactor fault
ï
Fault of control circuit
ï
Current detection circuit is damaged
ï
For three-phase input inverter input
phase loss fault occurs to power input
ï
Please check the
connection and connect
the wire properly
ï
Please check the
connection and mechanism
ï
Please contact the
supplier for repairing
ï
Please use inverter
with higher power
capacity
ï
Improve the
ventilation around the
inverter
ï
Replace the cooling fan
ï
Please seek technical
support
ï
Please seek technical
support
ï
Please detect at power
on after completely power
outage
ï
Please seek technical
support
Please check the motor's
ï
connection
ï
Input the correct motor
parameters (F08.00-
F08.04,F13.01-F13.05)
ï
Please seek technical
support
ï
Replace the contactor
ï
Please seek technical
support
ï
Please contact the
supplier for repairing
ï
Please check the three-
phase power input
ï
Please seek technical
support
12