Technical Specifications
ColorDisplay Series Thermostat Controllers
Touch Screen Series Thermostat Controllers
Power Requirements
Output Rating
Local Temperature
Sensor Type
Remote Temperature
Sensor Type
Wire Size
Temperature Adjustment
Range
Accuracy
Humidity
Deadband
Operating
Ambient
Conditions
Storage
Compliance
Dimensions
Shipping Weight
North American Emissions Compliance
United States
This equipment has been tested and found to comply with the limits for a Class B digital device pursuant to Part 15 of the FCC Rules. These limits are
designed to provide reasonable protection against harmful interference when this equipment is operated in a commercial environment. This equipment
generates, uses, and can radiate radio frequency energy and, if not installed and used in accordance with the instruction manual, may cause harmful
interference to radio communications. Operation of this equipment in a residential area may cause harmful interference, in which case the users
will be required to correct the interference at their own expense.
Canada
This Class (B) digital apparatus meets all the requirements of the Canadian Interference-Causing Equipment Regulations.
Cet appareil numerique de la Classe (B) respecte toutes les exigences du Reglement sur le materiel brouilleur du Canada.
20 - 30 VAC 50/60 Hz, 4.8 VA @ 24V nominal.
W1, W2, W3 = 0.4A max, 0.01A min, 3A inrush, 20 - 30 VAC
Y1, Y2, G = 0.8A max, 0.01A min, 3A inrush, 20 - 30 VAC
Thermistor, NTC 10K @ 25C
Thermistor, NTC 10K @ 25C
16 AWG (100 ft max) to 24 AWG (36 ft max)
35 to 99 deg F (2 to 36 degC)
35 to 65 deg F +/- 3 degF, greater than 65 to less than 80 degF +/- 2 degF,
80 to 99 degF +/_ 3 degF, greater than 99 to 104 degF +/- 5 degF
+/- 10% RH from 30-70% RH, 50-90F
Adjustable 1 to 6 deg first stage, 0 - 10 deg 2nd & 3rd stages
35 to 104 degF (2 o 40 degC), 5 - 95% RH non-condensing, 86 degF
max dew point
-22 to 122 degF (-30 to 50 degC), 5-95% RH non-condensing, 86 degF
max dew point
UL/cUL listed, file E107041, NEC Class 2
4.0" H x 5.2" W x 1.1"D
0.34 kg