unless press ON/OFF button.
In the process of unit operation, once the compressor runs continuously more than 6 min, the counter of stop-
working protection will be reset to zero and re-start a new counting process.
Note: For different models, I
6.2.10.4 IPM overheating protection
1. When IPM temperature T
protection.
≥95℃, the AC unit stops working for AC system protection.
2. When T
IPM
<87℃,and after compressor stopped for 3 min, can the unit be started to operate.
If T
IPM
3. If unit have 6 times of IPM over temperature stop working protection continuously, this protection can't be
recovered unless press ON/OFF button, and unit will show failure code.
In the process of operation, once the compressor runs continuously more than 6 min, the counter of over load
stop working protection will be reset to zero and re-start a new counting process.
The failure and times for protection will eliminate immediately once the unit to be switched off, or changed to fan
mode.
Note: If the defective failure can't be recovered, the failure can't eliminate even if operation mode changed.
6.2.11 Complementary
6.2.11.1 Energy saving (ECO)
Function effective on Cooling and Heating mode only.
On cooling mode, the set temperature range from 26℃ to 31℃,on heating mode, from 16℃ to 25℃.
6.2.11.2 TURBO
Function effective on Cooling, Heating, Fan and Auto modes, and fan speed operates on highest.
6.2.11.3 The communication control
If ODU PCB can't get signal feedback from IDU for 2 min continuously, AC unit stops working and shows E0 error
code as IDU/ODU communication failure.
Once the IDU & ODU communication recovery, and also the compressor stopped for 3 min already, can the unit be
recovered to operate.
Air Conditioner Service Manual
and I
have different programmed value.
LC
SC
≥87℃, the compressor will be frequency limited / reduced for IPM over temperature
IPM
22